Boiler Suggestion
S Davis
Member Posts: 491
What would you guy's use?
High mass cast iron rads in three story apartment building with a load of 650,000 Btu and DHW production this load is now powered by a 340,000 Btu AO Smith with a 200gal storage. by the way these numbers are output.
S Davis
Apex Radiant Heating
S Davis
A few smaller ones
A modular boiler arrangement. Assuming hot water system?0 -
System
Yes it is water system.
S Davis
Apex Radiant Heating0 -
Assuming the actual heating need is 600kBTU,
I would stage this across two modulating gas boilers. Pick different sizes like a M199 and a M399 and you have an incredibly wide range of BTU inputs (40kBTU-600kBTU). Combined with a Vision control package, you have redundancy, OR, and very attractive fuel savings.
Naturally, I would also throw in a Vitodens combo thus have several price points and options for them to chose amongst.
If oil is a possibility, I'd also stage multiple smaller boilers to better take advantage of OR, modulating water temperatures, etc.
BTW, your description confuses me. How is it possible for a house with a 650kBTU design-day loss to be heated by a single 340kBTU boiler?0 -
340
The 340K would be dedicated DHW.0 -
Aha...
Well, in that case, we'd better cover the building load and then add some.
You could do something very elegant like a four 200kBTU Vitodens' system with a cascading controller. Or, you could install a 200kTBU Vitodens for the first 200kBTU, followed by a VSB-13 (438kBTU) Vertomat for anything higher.
At a lower price point, four M199's or two Munchkin M399's combined with the Vision 2 system should also work great.
Combine any of these combinations with some intelligent piping to the heating system and you should have comfortable heat and a IDWH that "never" runs out of hot water. At 800kBTU input, the better IDWHs will produce over a thousand gallons of hot water per hour... For example, the Ergomax E109 has a continuous rating of 1379 Gallons/hour at 110°F rise. That's 23 gallons/minute...
The great thing about cast iron rads is the thermal flywheel they create... which leaves you more time to make up hot water as its needed for the DHW system.0
- 120 Geothermal
- 169 Indoor-Air Quality
- 396 Solar