Boiler Suggestion
S Davis
Member Posts: 491
What would you guy's use?
High mass cast iron rads in three story apartment building with a load of 650,000 Btu and DHW production this load is now powered by a 340,000 Btu AO Smith with a 200gal storage. by the way these numbers are output.
S Davis
Apex Radiant Heating
High mass cast iron rads in three story apartment building with a load of 650,000 Btu and DHW production this load is now powered by a 340,000 Btu AO Smith with a 200gal storage. by the way these numbers are output.
S Davis
Apex Radiant Heating
0
Comments
-
A few smaller ones
A modular boiler arrangement. Assuming hot water system?0 -
System
Yes it is water system.
S Davis
Apex Radiant Heating0 -
Assuming the actual heating need is 600kBTU,
I would stage this across two modulating gas boilers. Pick different sizes like a M199 and a M399 and you have an incredibly wide range of BTU inputs (40kBTU-600kBTU). Combined with a Vision control package, you have redundancy, OR, and very attractive fuel savings.
Naturally, I would also throw in a Vitodens combo thus have several price points and options for them to chose amongst.
If oil is a possibility, I'd also stage multiple smaller boilers to better take advantage of OR, modulating water temperatures, etc.
BTW, your description confuses me. How is it possible for a house with a 650kBTU design-day loss to be heated by a single 340kBTU boiler?0 -
340
The 340K would be dedicated DHW.0 -
Aha...
Well, in that case, we'd better cover the building load and then add some.
You could do something very elegant like a four 200kBTU Vitodens' system with a cascading controller. Or, you could install a 200kTBU Vitodens for the first 200kBTU, followed by a VSB-13 (438kBTU) Vertomat for anything higher.
At a lower price point, four M199's or two Munchkin M399's combined with the Vision 2 system should also work great.
Combine any of these combinations with some intelligent piping to the heating system and you should have comfortable heat and a IDWH that "never" runs out of hot water. At 800kBTU input, the better IDWHs will produce over a thousand gallons of hot water per hour... For example, the Ergomax E109 has a continuous rating of 1379 Gallons/hour at 110°F rise. That's 23 gallons/minute...
The great thing about cast iron rads is the thermal flywheel they create... which leaves you more time to make up hot water as its needed for the DHW system.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements