Knight Boiler Install (Residential) Job Pics
In HotRod's diagram...
What is that to the right of the Knight boiler and how does it attach to the rest of the heating circuit? By ordinary tee's? monoflows? other?0 -
IndirectDomesticHotWater...
its pump is run by a separate set of contacts on the boiler, and the boiler shuts off the space heating pump contacts at that point and brings its temp up to whatever you set it for in the DomesticHotWater settings and for as long as you set the hot water priority's duration for, with 30min being the default
oh yeh, regular tees, and spring checks - i usualy put 4 spring checks, supply/return of both heat and hot water circuits - to lock down any heat migration - in this actual setup - there was natural up/down heat traps so they only used the checks in the pumps0 -
if you can find the time to go to locinvar...
You will be duly impressed I guarantee it!!!0 -
paul, what was the name of that tool...
to cut off threaded rod??
thanks0
- 167 Indoor-Air Quality