Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
R7148 answer
don_182
Member Posts: 69
I always thought if the controller was seeing a flame or any
light for that matter it would not start the fring squence.
light for that matter it would not start the fring squence.
0
Comments
-
R7148 answer
A couple weeks ago there was a question about the R7148. It took awhile to network. This is from the product engineer:
The R7184 has diagnostic features that help to trouble shoot. I would like to know what the flash code for the green LED was when the control went dead. I would bet it was in a lockout state due to the limited recycle or limited reset mode and the contractor did not read the instructions to hold the red button down for X seconds to reset it.
The cad cell readings during run and the cad cell reading during Off would be important. In addition what the AF2 burner was firing into, ie is the chamber lined with a wet pack or is it a steel unlined chamber, could be that the control is seeing flame either during valve on delay or burner motor off delay due to a valve problem---
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements