Primary/Secondary with Mod-Cons Part IV
Mike T., Swampeast MO
Member Posts: 6,928
Attached are the revised full-load system, such at half load (defined as 1/2 the full-load btu/sq.ft output) and a flow diagram.
Only major change to the full-load system was in the master suite where I dropped the plus carpet and considered hardwood with large area rugs (hopefully not too large if wool ;0) I also found two relatively minor errors--one in delta-t for one zone (I used half), the other in the total gpm requirements (I forgot to re-total after the change in the garage).
You'll have to tell Acrobat to rotate the flow diagram--sorry.
Personally, I consider 50% load to be a reasonable representation of true <I>outdoor design condition <B>maintenance</B></I> load for a RFH home with loss based on Manual-J. Literature and studies from Danfoss and others [seems] to validate this assertion.
<B>Actual</B> supply temp requirements in the "high temp" zones vary from 97°F to 109°F. The garage (now assumed 62°F ambient) still causes problems however as its supply requirement drops to a mere 70° with 81°F required for the bulk of the basement.
I did my best to normalize output of the zones (both in high and low temperature groups) to the same supply temp. This is an attempt at a snapshot of what would happen if ALL zones called simultaneously <I>just to maintain their desired settings</I>. Obviously, this CAN'T happen for any length of time as some zones (especially the garage) are relatively over-supplied with heat when all supply temps are equal.
I do ask that you pay particular attention to the flow diagram. Please check for errors. I've done my best to double- and triple-check, but sometimes stupid things pass me by...
Note that not only is the system supplying significantly more energy than required to <I>maintain</I> all zones, but that it is IMPOSSIBLE for the boiler (with fixed flow) to produce this condition--the output is EVEN GREATER if the supply temperature <I>at the low-loss header</I> is to be maintained.
Next, I'll re-design with flow-setters in an attempt to design for flow more in line with requirements. Of course there will still be that pesky little problem of zone delta-t dropping by approximately 50% as load drops by 50% with flow remaining constant...
Only major change to the full-load system was in the master suite where I dropped the plus carpet and considered hardwood with large area rugs (hopefully not too large if wool ;0) I also found two relatively minor errors--one in delta-t for one zone (I used half), the other in the total gpm requirements (I forgot to re-total after the change in the garage).
You'll have to tell Acrobat to rotate the flow diagram--sorry.
Personally, I consider 50% load to be a reasonable representation of true <I>outdoor design condition <B>maintenance</B></I> load for a RFH home with loss based on Manual-J. Literature and studies from Danfoss and others [seems] to validate this assertion.
<B>Actual</B> supply temp requirements in the "high temp" zones vary from 97°F to 109°F. The garage (now assumed 62°F ambient) still causes problems however as its supply requirement drops to a mere 70° with 81°F required for the bulk of the basement.
I did my best to normalize output of the zones (both in high and low temperature groups) to the same supply temp. This is an attempt at a snapshot of what would happen if ALL zones called simultaneously <I>just to maintain their desired settings</I>. Obviously, this CAN'T happen for any length of time as some zones (especially the garage) are relatively over-supplied with heat when all supply temps are equal.
I do ask that you pay particular attention to the flow diagram. Please check for errors. I've done my best to double- and triple-check, but sometimes stupid things pass me by...
Note that not only is the system supplying significantly more energy than required to <I>maintain</I> all zones, but that it is IMPOSSIBLE for the boiler (with fixed flow) to produce this condition--the output is EVEN GREATER if the supply temperature <I>at the low-loss header</I> is to be maintained.
Next, I'll re-design with flow-setters in an attempt to design for flow more in line with requirements. Of course there will still be that pesky little problem of zone delta-t dropping by approximately 50% as load drops by 50% with flow remaining constant...
0
Comments
-
Why?
Why do I have the feeling that this is going to go somewhere else?0 -
If by "somewhere else" you mean the fallacy of trying to maintain a reset curve target in a multi-zoned system with fully fixed flow you have an idea where I'm going...
I already said that I suspect such is impossible. This is just the first step. I'll try to improve but I seriously doubt it will get much better...
Please prove me wrong.
0 -
thats interesting
so, you are suggesting that ALL radiant floor systems are being oversized by 50%?
0 -
Buddha says
Everything must stay in harmony. Flow gentler...0 -
Again, PLEASE look for errors, stupid or otherwise.
Those with "Siggy software" have no problem. Do you find the same results?0 -
Actually....
I would guess that it is a factor of 5 to 10 times as inefficient as they could and should be. The circs won't be as reliable so why would a manufacturer risk their name putting them out there? This may very well be the case here. This change increases their complexity severalfold yet this is all to save $20 to $25 a year? And worse yet, more service calls that are lost time charges.0 -
NO!
I'm suggesting that ALL systems no matter how well designed are oversized in the range of 40% - 55% based on the ability to maintain desired setpoint in normal conditions.
Manual-J and all other WELL DESIGNED "heat requirement" calculations provide the necessary and required uncertainty factor to include reasonable occupant desires. ZERO need to increase above!!!
0 -
with that general idea in mind...
just how much leeway are you suggesting we use for the ability of a homeowner to control a zone other than by a specific set point control when they wish to change the setpoint temps while they are in"The Zone" ?
is the 72 degree F a hoped for designe point that will allow the change to cover the anomalies of the particularly eccentric?
if the 85 % thing is true then there seems to be 15 percent of some somewhat "different " individuals that seem to have their own particular take on comfort...
do you recall the 40 zone home i posted a while back.....the Lady of the home dials zones up and down and curiously seems to have no set pattern of just what or where she will be next..:) i hope you do not find that offensive or derogatory ,..shes just a bit different...0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements