Hyrdronics Design Studio Question

hr
hr Member Posts: 6,106
that question to Siggy. Is this the concept you are looking for?

http://www.pmengineer.com/CDA/ArticleInformation/features/BNP__Features__Item/0,2732,132159,00.html

hot rod

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Cosmo_3
    Cosmo_3 Member Posts: 845


    I am trying to use my new Pro version software to help in designing a system. I want to add 5 hot water coil circuits, and do not see that option under heat emitters. I was looking for a way to add a custom emitter using flow required, head, or Cv, but can't figure it out. Anybody out there who has the software, please help. I will call Siggy at Appropriate Designs, but I assume they are not open until monday.


    Cosmo Valavanis

    Dependable P.H.C. Inc.
  • thp_8
    thp_8 Member Posts: 122
    # of branch curcuits add

  • Cosmo_3
    Cosmo_3 Member Posts: 845


    Huh? I'm sorry, I know how to add branch circuits. It's just the only options for heat emitter are baseboard, or radiant. I want to use hot water fan coils.

    Cosmo Valavanis

    Dependable P.H.C. Inc.
  • thp_8
    thp_8 Member Posts: 122
    What

    Add your 5 circuits, then click show balance valves and adjust as needed.
  • hr
    hr Member Posts: 6,106
    I don't know

    that you have other choices.

    Could you just build baseboard to the spec of the fan coil?

    Say the output is 10,000 BTU/hr at 1 GPM. Insert the BTU of the FC, and adjust flow rate via the box?

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Cosmo_3
    Cosmo_3 Member Posts: 845


    Well, I have 5 hot water coils, 90K BTU each, each coil needs 10 gpm, and per aquecoil literature, every TE4 coil itself needs 4.9 Pump head (feet), add to that about 4 ft of head for branch piping from the main. I want to design the system to use a single, variable speed circ controlled by a pressure differential sensor to maintain a constant pressure. I can figure it my old way, but was wondering how I could use my Hydronic Suite program to simulate it.

    Cosmo Valavanis

    Dependable P.H.C. Inc.
  • thp_8
    thp_8 Member Posts: 122
    Did you find it ?

    I think this is close minus the vari. circ.
  • Cosmo_3
    Cosmo_3 Member Posts: 845


    yes, I was able to play withe the Cv ratings. Pretty cool program to play with, can't wait for some updates. Thanks for all ou help thp, and hot rod


    Cosmo Valavanis

    Dependable P.H.C. Inc.
  • Bob Sweet
    Bob Sweet Member Posts: 540
    Just ordered the Design Studio,

    can't wait till it gets here.