Can someone tell me how to determine the correct settings for the Honeywell Triple Aquastat High, Low and Differential. What are best settings for cold weather?
0
Comments
-
It depends...
Assuming an American cast iron boiler, set low for around 140 degrees F, high limit for 180 degrees F with a 10 degree delta T. That should keep you out of trouble, yet in hot water.
If it's a copper fin tube boiler, your low could be maybe 10 degrees F lower.
If its a Buderus boiler, low can be set for 107 degrees F.
Stay warm!