ASME requirements for expansion tank
Rocky_2
Member Posts: 89
Under what conditions do I need to use an ASME rated expansion tank on a boiler system?
ASME
I believe it is required in systems where the pressure relief is above 30 #, but the local jurisdiction may have more in mind. Also, when installing an ASME expansion tank and you isolate the tank from the boiler relief (ball valve,ect) you are required to install a relief on the ex. tank. Marc0 -
what do
What do or how reilef valve will work on ex tank if the ball valve is closed, there no pressure change unless the fill valve is on the tank side of valve and opened...0 -
The General Rule is
any tanks rated over 15 PSI would need to be ASME stamped; however, there may be exceptions for small volumn tanks such as those used for home boiler systems.
I'll send an email to myself at work and if I get time - or the right person is in today - I'll either look it up or ask. The ASME code books are no less than 20 ft from me (and we probably have over 1/2 of the code books in the ASME series at work; even multiple copies of some of the sections).
If there is a small volume exemption - I'll let you know the cut off size.
Perry0 -
Temperature
If I gather the situation you are describing, that the ball valve is the fill source which is closed. Any captive volume of water requires a relief valve and expansion tank, the pressure increase (or decrease but who cares?) is due to thermal expansion. Boyle's Law.0 -
Public or Commercial Work
Any public facility or commercial work gets an ASME H-stamped tank (all unfired pressure vessels for that matter) in our office. Given that is practically all of our projects, they naturally all get them.0 -
Two and a half times the...
working pressure of the boiler.
That is the req. in the great state of Colorado. If the boiler has a 30psi relief valve (AND THE RATINGS PLATE SAYS 30PSI):
30 times 2.5 = 75 you can use a non-ASME tank.
If the boiler has a 50 psi relief valve (AND THE RATINGS PLATE SAYS 50PSI)
50 times 2.5 = 150 ..you must use an ASME tank.
This came straight from the State Boiler Inspector Randy Austin (This was about a year ago when I spoke to him)
A.S.M.E = ALMOST, SOMETIMES, MAYBE, EXCEPT
the relief is for excessive pressure during a fire. (inspector explained this) since you have a normal tank inside of a armour plated tank. the theory as i was told is during a fire the ASME tank could reach explosive temperatures, then the fireman sprays water on the tank and boom!!! during the fire someone must also turn off the service valve on the ASME tank. Very unlikely, but still required in at least one area we work in. this inspector is mostly commercial and stays ontop of the codes, unlike most of the others who allow just about anything. marc0 -
A.S.M.E.
Almost. Sometimes. Maybe. Extortion fees.0 -
What the Authorized Inspector said:
For home heating applications state and local exemptions dominate in the US, regardless of the ASME code. Not all states have adopted the code either (even for huge pressure vessels or for Section III and Section XI which is nuclear vessels and nuclear inspection programs).
If the state has adopted ASME code, or at least Section VIII in its entirety, there are exemptions for vessels under 6", exemptions for small volume (several cubic feet) under a modest pressure (but the AI did not know the pressure off the top of his head), and other exemptions that may apply to air bladder over water (well water and home heating systems).
I could not locate a current code year Section VIII in the few minutes I had to look at the exact exemptions in Section VIII today (otherwise, it was a 12.75 hour day with lots left todo over my "free" weekend).
Key here is to check the local regulations.
Commerical work and apartment buildings almost always need code stamped vessels.
Perry0 -
service supervisor
need to know what the requirements are for asme expansion tanks in college buildings in Burlington Vermont0 -
what Perry says but....
Whatever the guy in charge says. What about a repurposed boiler, for example. Originally used for process work it has an ASME 50 psi plate on it. Now used only for heating and has 5 psi pressure relief safety. Insurance inspector points to ASME stamp and demands 75 psi static test. What to do ?0 -
Re: asme req on expansion tanks
City of Seattle adopted the asme code. This is how they read it. if a boiler is limited rated at 200,000 btu input or under and is limited to 210 degrees or under a non asme expansion tank may be used unless in a place of public assembly or place of worship???? don't know why. Then only if it is under 2.5 or 3 ?? (can't remember) cft of volume on tank can it be non code tank. In all other occupancies the above input and temps govern it "except" if tank is under 5 cubic feet or appx 33 galons a non code tank can be used. That is how our jurisdiction reads the asme code. side note: tank must be rated for boiler max wp also. Good luck, Tim0
- 86.9K THE MAIN WALL
- 57 Biomass
- 110 Chimneys & Flues
- 5.7K Gas Heating
- 106 Geothermal
- 70 Pipe Deterioration
- 978 Plumbing
- 6.3K Radiant Heating
- 387 Solar
- 15.4K Strictly Steam
- 44 Industry Classes
