Loop Lengths

Joe_20
Member Posts: 25
So, I have a 1000 foot roll of 3/8" PEX tubing and want to begin installation. The "design" calls for loop lengths to be approximately 200 foot. How "exact" does this have to be? What's the best way to measure and is ± 25 feet close enough? Have a great day!
0
Comments
-
i dont use 200 ' lengths however it will depend on a couple
things...1 might be the means you are controling flow and temp another might be the reason for the heat loss designe and lay out in the first place...so i would say it depends...my thought goes like this 'put it in the slab dont just chop off any random length You Feel like.'.."i dont care.. take it up and do it right "and "Ripp it Out!" these are two things that i have said...ripp it out because of a nick in the pipe...i have no affinity for putting a coupling in a slab....0 -
variance
Keep the variance of lengths to no more than 10% over all.
so.. for 200ft lens., no longer than 220, no shorter than 180'
If you vari more than this it will be more difficult to balance at the end of the day.
hope this helps
EINSIEDLER
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 948 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements