1 or 2 steam risers?
bovide_4
Member Posts: 161
When is it advisable to use 1 or 2 steam risers from the boiler to the header?
Boiler in question is a Burnham 904. The tappings are 4".
Boiler in question is a Burnham 904. The tappings are 4".
0
Comments
-
risers
simply follow the piping diagram from manufacturer0 -
I read the manual cover to cover. 90% of the content is about hot water boiler piping.0 -
The information
you are looking for is on or about Page 35 of the Installation Manual and is entitled Figure 34. We only call for a single riser on that size boiler and that should be 4" as well as a 4" header. The equalizer and return needs to be 2". Hope this helps.
Glenn Stanton
Manager of Training
Burnham Hydronics
www.burnham.com0 -
You are correct. Many thanks.0 -
Glenn, its because
you guys in the factory end allow one riser that people will use one riser..two is better and everyone knows it..we end up going out and fixing problems cause the boilers were only plumbed out one side..we fix it by plumbing from both sides..wait a minute..thats a good job for us...never mind..gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Gerry
I won't argue a bit that more is probably better, but in reality one riser, properly piped and sized, is suffice for the smaller size boilers to deliver the steam to the system mains sufficiently and effeciently.
Glenn Stanton
Manager of Training
Burnham Hydronics
www.burnham.com0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 99 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements