1 or 2 steam risers?

bovide_4
bovide_4 Member Posts: 161
When is it advisable to use 1 or 2 steam risers from the boiler to the header?
Boiler in question is a Burnham 904. The tappings are 4".

Comments

  • bob young
    bob young Member Posts: 2,177
    risers

    simply follow the piping diagram from manufacturer
  • bovide_4
    bovide_4 Member Posts: 161


    I read the manual cover to cover. 90% of the content is about hot water boiler piping.
  • The information

    you are looking for is on or about Page 35 of the Installation Manual and is entitled Figure 34. We only call for a single riser on that size boiler and that should be 4" as well as a 4" header. The equalizer and return needs to be 2". Hope this helps.

    Glenn Stanton

    Manager of Training

    Burnham Hydronics

    www.burnham.com
  • bovide_4
    bovide_4 Member Posts: 161


    You are correct. Many thanks.
  • gerry gill
    gerry gill Member Posts: 3,078
    Glenn, its because

    you guys in the factory end allow one riser that people will use one riser..two is better and everyone knows it..we end up going out and fixing problems cause the boilers were only plumbed out one side..we fix it by plumbing from both sides..wait a minute..thats a good job for us...never mind..
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Gerry

    I won't argue a bit that more is probably better, but in reality one riser, properly piped and sized, is suffice for the smaller size boilers to deliver the steam to the system mains sufficiently and effeciently.

    Glenn Stanton

    Manager of Training

    Burnham Hydronics

    www.burnham.com