Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Multi-zone primary-secondary help...

Options
hvacfreak
hvacfreak Member Posts: 439
I am building a multiple zone manifold (injection) and I have chosen to drop from the the bottom of the main and thermal trap up ( 12 inches ) with the circuit take-offs. The last job I did with multi-injection we came out of the top of the main and actually had flow through some zones that were not calling ( I did not select the circulators , and yes we had 6 inches center to center on suply / return take-offs. ). Right now the manifold is just copper pipe ( no components installed ).

Will my thermal traps help avoid this unwanted flow possibility ( Dan's book says no , lol..but I ordered it too late )? Should I plan on check valves on both supply and return take-offs ? I just want to use on/off ( not variable )control circulators ( or is this where I'm kidding myself ). All replies appriciated.
- Mike

Comments

This discussion has been closed.