Multi-zone primary-secondary help...
hvacfreak
Member Posts: 439
I am building a multiple zone manifold (injection) and I have chosen to drop from the the bottom of the main and thermal trap up ( 12 inches ) with the circuit take-offs. The last job I did with multi-injection we came out of the top of the main and actually had flow through some zones that were not calling ( I did not select the circulators , and yes we had 6 inches center to center on suply / return take-offs. ). Right now the manifold is just copper pipe ( no components installed ).
Will my thermal traps help avoid this unwanted flow possibility ( Dan's book says no , lol..but I ordered it too late )? Should I plan on check valves on both supply and return take-offs ? I just want to use on/off ( not variable )control circulators ( or is this where I'm kidding myself ). All replies appriciated.
- Mike
Will my thermal traps help avoid this unwanted flow possibility ( Dan's book says no , lol..but I ordered it too late )? Should I plan on check valves on both supply and return take-offs ? I just want to use on/off ( not variable )control circulators ( or is this where I'm kidding myself ). All replies appriciated.
- Mike
0
Comments
-
There is some science to thermal drops
merely droping the pipe below the P/S connection may not cut it. Ask me how I know.
An astute hydronic contractor wiz in upstate NY was able to shine the light for me. Thanks Harvey.
Check out this article before you
proceed.http://www.pmmag.com/CDA/Archives/2df7e8c55e028010VgnVCM100000f932a8c0____
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
it seems....
that I missed the boat on my way of thinking. Thanks for that information.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements