taco circulators
grindog
grindog Member Posts: 121
what taco circ is the best to use in indirect water heater applications have a fourty gallon tank next to boiler what size should i use
  • grindog
  • Al Gregory
    Al Gregory Member Posts: 259
    a 007 should work fine
  • Joe Mattiello
    Joe Mattiello Member Posts: 752
    Taco, 007-F5-IFC in most cases
    The Taco, 007-F5-IFC will do a nice job in most cases. However, to size pump properly you need to know the pressure drop across the coil. The 007 IFC with the integral flow check will out perform the standard 007, because you do not have the pressure drop across the flow check, which can be as high as 63 ft, for a 1". Additionally, the IFC saves time, and money. The way I look at it is more money for Sundays Super Bowl Party!! Go Pats!! Attached is the submittal data information for the 007
    Taco, Inc.
    Joe Mattiello
    Technical Service Technician
    joemat@taco-hvac.com
    401-942-8000 X 484
    www.taco-hvac.com
    Joe Mattiello
    Taco Comfort Solutions
  • EJW
    EJW Member Posts: 321
    Taco circs
    I install Vaughn Top Performers and always use 008. EJW