After installing new vents on the mains and lowerin the pressure a bit, I am amazed at how quickly my radiators heat up and how much less hot my basement is. Thanks for the advice Steamhead.
Today I installed a Gorton 4 vent on two radiators that before were not getting enough heat. Now everything is heating equally except for one tiny bathroom radiator that is getting zero steam. I even took the vent off to see if it would get steam but the temperature never elevated a degree.
Does this mean that the two new vents that I installed are venting too much? Is the problem that the pressure differential is too low, so the pressure isn't being maintained long enough to reach this one radiator, which by the way, is not on the far reach of the line, but on a riser to the first floor mid-way down the main line.
Thanks
Today I installed a Gorton 4 vent on two radiators that before were not getting enough heat. Now everything is heating equally except for one tiny bathroom radiator that is getting zero steam. I even took the vent off to see if it would get steam but the temperature never elevated a degree.
Does this mean that the two new vents that I installed are venting too much? Is the problem that the pressure differential is too low, so the pressure isn't being maintained long enough to reach this one radiator, which by the way, is not on the far reach of the line, but on a riser to the first floor mid-way down the main line.
Thanks
0
Comments
-
Correction: It was the GORTON D Vapor Equalizing Valve0 -
The radiator that is not heating was plenty hot before I added the faster vents on the other two radiators.0 -
That might be part of the problem
but I'd also ask if the mains are insulated, and if the boiler is properly sized to the radiation.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
The main pipes are insulated, but the riser to the radiators are not. The boiler is way oversized - 70years old. When I replaced the main vents yesterday, one of them wasn't venting at all.0 -
Then
experiment with your vent sizes. Try going one size smaller on the rads that heat fast and see if the steam reaches the cold one.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I have to thank you for all your advice. You've been so helpful!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements