steam vacuum

dave_20
dave_20 Member Posts: 5
Hey guys,
In this area there is very little steam heat. I may see one a year. What would make a steam boiler fall in to a vacuum? I had one the other day that was in a vacuum and when I opened the blow down valve air rushed in and the system settled.
Thanks,
Dave

Comments

  • Mark Hunt
    Mark Hunt Member Posts: 4,908
    Zone valves


    If someone added zone valves to the system that could do it.

    What type of steam system is it?

    Mark H

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Jamie Hall
    Jamie Hall Member Posts: 24,838
    vents

    how are the main vents? If they (or it!) are bad, that could do it too... also, I've heard that some main vents if they get too hot will not open on vacuum; they should be far enough from the return (if you have them on the return!) that steam can't hit them...

    On the other hand, some vapour systems are designed and intended to pull a slight vacuum. Could it be that?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • dave_20
    dave_20 Member Posts: 5
    steam vacuum

    mark,
    it is a pennco boiler, two-pipe. no zone valves.
    thanks,
    dave