Combustion analysis question

Aside from O2, CO2, CO, draft, smoke test and net stack temp in the breech, why would a CO2 reading "over the fire" make sense? Seems to me that a reading taken there won't add anything of substance and may well be dilluted by free air.

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=98&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • jim sokolovic
    jim sokolovic Member Posts: 439
    It could tell you...

    if there is significant leakage around the boiler sections and flue collector. The CO2 in the breech would be the diluted reading, in that case?
  • Rudy
    Rudy Member Posts: 482
    Getting accurate stack readings

    Yep, you might want to take an O2/CO2 reading over fire (with the opening sealed with aluminum foil or something) and compare it to the stack readings.

    I've found that in a tight system the stack reading will normally be about 1/2% higher.

    Any more difference than that indicates that there is alot of 'tramp' air being sucked in though cleanout ports, access doors, etc. and the stack reading is not accurate.