Wasn't there a post awhile back about pipe wall thinning in a domestic recirculating system? I thought somebody listed a website for ideas to solve problem. I have a 5 story nursing home with 4 006's on 5th floor flowing down and there's a B&G HV in 1st floor mech. room getting a lot of leaks and interior of pipe etched.
0
Comments
-
H.E.C....
Hydraulic Erosion Corrosion. The best example of HEC I can conjur up is the Grand Canyon.
1. Make sure the veolicty is maintianed at the minimum velocity for the pipe size. (2 foot per second)
2. Install aquastats so that when water comes back adequatley hot, the pump shuts off.
3. Install a timer to allow the pumps to run only during usage periods.
Note also that petroleum based fluxes will do the same thing the HEC does...
Why the 006s and the HV? Sounds like mega engineering overkill to me, but then again, I'm not looking at the system.
Got schematics?
ME
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
this product could solve your problem
Check out Copperknight.com0 -
.
what mixing valve do you have ? if its a Holby --the oldman who used to make them in his basement-says-you need constant circulation or the elements burnout0 -
Copper
This may be elementary,I remember hearing of a major casino in Vegas having seriuos problem similar to this due to copper pipe not being reamed prperly.0 -
www.copper.org
you will find plenty of info on copper pipe at this site.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements