OVERHEAD OIL LINES
paul sr
Member Posts: 39
Ok, tell me if this makes any sense.Myself and another oil tech were talking about overhead two pipe oil lines. He says that on a two pipe, overhead oil line feeding off the top of the tank, he opens the bleeder puts the hose in a bucket, puts his finger over the end of the hose and he seems to think bye doing this its going to make the pump pull harder. Does this really affect the pull?
0
Comments
-
He's wrong!
Here's how you bleed with an overhead line or an osv.
Put the bleeder into a pail with a wrench on the end, air can get violent (see purge-bleed on pumping away). Leave the valve at the pump open and the bleeder closed. Go to the tank and close the valve.
The 'kitty' in the pump will wake up and when she really starts to scream (20" Vac.) open the valve and walk back to the pump. By the time you get there the pump will be power/vacuum bled.
Like most things, this ain't new, you just have to know where to find it. It's in a couple of my books and you can watch a video on this if you can find an old copy of Webster pump's 'Heart of an Oil Furnace', FACT!
www.FiredragonEnt.com
0 -
Confused
How does the pump get purged if you closed the bleeder
screw on the pump and never reopened it based on what I read. What did i miss.
marty
0 -
two pipe oil lines
Marty, if this was single pipe overhead line ,yes you would have to open the bleeder, however, with two pipe this will almost always self bleed through the return line . .......
mike0 -
two pipe oil lines
Marty, if this was single pipe overhead line ,yes you would have to open the bleeder, however, with two pipe this will almost always self bleed through the return line . .......
mike0 -
two pipe oil lines
Marty, if this was single pipe overhead line ,yes you would have to open the bleeder, however, with two pipe this will almost always self bleed through the return line . .......
mike0 -
ooops!
sorry, must be my nervous condition0 -
My oversite
You are right, it was late, I missed the 2 pipe part.
Hope you are not made nervous by idiot's like me (8-)
thanks for waking me up.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 65 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements