circulatorsMy home has forced hot water oil heat. The house has
vbacon
Member Posts: 2
My home has forced hot water oil heat. The house has 3 zones and three
circulators. My question is / is one circulator better than three? my problem
,if the heat is coming up and you are taking a shower there is no hot water
is there a way to prioritize?
Any info would be helpful
Thanks
vap55@cox.net
circulators. My question is / is one circulator better than three? my problem
,if the heat is coming up and you are taking a shower there is no hot water
is there a way to prioritize?
Any info would be helpful
Thanks
vap55@cox.net
0
Comments
-
My home has forced hot water oil heat. The house has 3 zones and three
circulators. My question is / is one circulator better than three? my problem
,if the heat is coming up and you are taking a shower there is no hot water
is there a way to prioritize?
Any info would be helpful
Thanks
vap55@cox.net
0 -
SR503/with priority
Try using the Taco switching relay with the priority feature. For your reference I have attached the submittal data information. Taco, Inc.
Joe Mattiello
Technical Service Technician
joemat@taco-hvac.com
401-942-8000 X 484
www.taco-hvac.comJoe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
no domestic hot water
In answer to your question, "Yes" you can prioritize the domestic hotwater and it should be.
What manufacture of controls are on your boiler? Usually we find Honeywell controls as OEM. That being the case, the R8124 triple acting aquastat will have "ZC and ZR" terminals on it. These two terminals should be wired correctly into the R845 relays (or something similar)of the other two circulators.
Sometimes an installer will wire in an R89 relay and you'll lose priority for domestic hotwater.
Hopefully it is a simple wiring job. Have a qualified service tech check it.
Good Luck
Dave
www.trainingontheroad.com0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements