A question about Circulators on Packaged Boilers
Comments
-
Glenn
That's the method we usually employ. What is your opinion of 24V vs 120V LWCO's? I ran into two situations where a 24V model has failed to detect the presence of fluid. One was an Erie and one was an M/M. Both times, the probe was covered with gunk. I have however, seen 120V units in much worse shape and still function. Just a fluke or are the 24V jobs more prone to fail?0 -
We would
rather see the 120v models simply to avoid cutting into the factory wiring harness and for the reason already stated. I am unaware of any difference in actual performance between the two though on that side of the circuitry. Just to satisfy my own curiousity, I will contact our friends at Hydrolevel and see if there is any difference in the actual operation on that side.
Glenn0 -
why not
just use a tekmar relay, to open the main 110v ciculator supply line - and hook the relay up to a rb55
and make sure the cut-off is vented - "and have a nice day"
the reason for doing it this way is to preserve the power in the rest of the stuff for time and programming0 -
Sure pretty
but....wouldn't it have been easier to just use a 120v model to interupt the hot leg to the 361 and relays? That is all you are doing anyway with the extra relay at great expense I might add.
Glenn0 -
i wish you were right, but the 120v model avail
was almost twice as expensive as the rb55 and the relay, - (which wasnt actually a tekmar but rather the same exact OMRON relay from GRAINGER at half the price), and the 120v model was also huge - cause the minute you go to high voltage - the whole wiring arrangement is different especially around water - the "triac" electronic switch inside the rb55 could handle 120v/15a, provided you had a large enough heat sink and a beefy electrical connection
my personal preference is to keep the 120v wiring in a boiler room down to a minimum - i would rather see a 1000va 24v buss in the boiler room with 24v multi-phase brushless-DC electronic drive vari speed pumps - call me "new school" though we should have gone to 48v a long time ago, 48v is still safe to handle raw, and gives a much better power to copper size ratio than 24v cars makers plan to phasing that in, in the near future with the advent of hybrid-electrics
0 -
Steve, if the probe
is coated with gunk you need a good cleaning and flush. Really shouldn't be that much gunk in the system to render ther probe ineffective. If so your heat exchange surfaces in the boiler are getting compromised, by the sludge also..
I think the 120 volt have a more sensitive probe, also. I know there was a different sensor spec on the model 120 compared to the 120II. Although my brochures are pretty old, this may have changed.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Armstrong bearing assembly failure
Bearing assembly failure.
I have replaced 3 Armstrong bearing assembly in the last 6 mouths, the last one lasted 2 mouths. The bearing assembly model # M 810 126 507. The pump is on 24-7
I would like to put a pro in tank, when no call, pump will be off. I suggested to maintenance supervisor.
The pump is installed on a Lochinvar Power-fin boiler, between a 200 gal storage tank 2 inch piping . Tank is with in 5 feet of Boiler. Boiler size 745. 000 BTU providing domestic hot water.
The first bearing assembly lasted between 04 to 2011, Last 2 lasted 6 mouth.
Any help would be appreciated.0 -
Armstrong bearing assembly failure
Bearing assembly failure.
I have replaced 3 Armstrong bearing assembly in the last 6 mouths, the last one lasted 2 mouths. The bearing assembly model # M 810 126 507. The pump is on 24-7
I would like to put a pro in tank, when no call, pump will be off. I suggested to maintenance supervisor.
The pump is installed on a Lochinvar Power-fin boiler, between a 200 gal storage tank 2 inch piping . Tank is with in 5 feet of Boiler. Boiler size 745. 000 BTU providing domestic hot water.
The first bearing assembly lasted between 04 to 2011, Last 2 lasted 6 mouth.
Any help would be appreciated.0 -
Bearing failures:
I don't know what your Armstrong pump is but bearing and seal failures that continue are usually caused by the motor mpount/bearings being worn and causing ossculattions in the moter whigh the bearing doesn't like. If it is a larger commercial tyle, mounted on a skid, the motor and wet end are not aligned but that usually k\just lunches the coupler. If the Armstrong circulator is an antique, and you are having problems with the bearings and seals, change the motor bearings or change the motor.
A problem seen on old 3 piece circulator but not often seen on wet rotar circulators.0 -
Turn it off
I do not know the reasoning behind "always on" hot water boilers and pumps. It make tank stratification impossible and tend to wear the pipes, pumps and boilers.
I recently put a tekmar 150 setpoint controller on the tank and used it to turn off the boiler which in turn controls the pump. The nice part is you can set the differential to get the optimal cycle time."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
armstrong bearing assembly
Plugger, contact me at rhalvorsen@armlink.com and lets see if we can get to the bottom of these failures,our local rep or service department can usually solve these problems quickly0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements