Three way mixing valve sizing
Mike Lundstrom
Member Posts: 10
I am trying to figure out if there is a consistent way to size three way mixing valves. I would like to size a valve for an air handling unit in a school we are renovating and need some help. I have seen large pipes ran to small valves and looking for some background info. What info do I need to know? How does the Cv rating work into all of this? Is there some good resources I may be able to track down? Any help would be appreciated.
Mike Lundstrom
Mike Lundstrom
0
Comments
-
When sizing ESBE three way mixing valves we use the following: 1 to 8 GPM = 3/4" valve, 9 to 14 GPM = 1" valve, 15 to 22 GPM = 1.250" valve, 23 to 40 GPM = 1.5" valve, 41 to 60 GPM = 2" valve.0 -
Valve Sizing
Call me, I can work you through it. 800-321-4739
Tim D.0 -
Short strokes...
Here's some general stuff to consider which Tim can go into detail when you call him up...
Valves and heat terminal units have performance personalities and much like people are not the same.
In fact for valves, there are roughly five different 'personalities' determined by the shape of its plug . (Quick opening, linear, logarithmic & its cousin equal percentage, and split characteristic)
These valve personalities can be influenced by the speed of the stem stroke, the rangeability of the linkage and control and the minimum controllable flow specification provided by the manufacturer.
Fan/coils can have an infinite # of personalities depending on one of the conditions below:
Constant flow, variable temperature
Variable flow, variable temperature
Constant flow, constant temperature
Variable flow, constant temperature
You've no doubt heard the saying that opposites attract one another?
The same is true with matching a valve to a fan/coil. (or any heat terminal unit for that matter)
For example, a coil designed at 180 deg f, for a 20 degree delta t has postal performance which means it actually reaches close to 70% nominal output with only 17% nominal flow.
To linearize the output, ie: 50% output at 50% flow, one has to select a valve/actuator/control combination which is opposite in performance to the fan/coil(think laid back surfer dude) ie: having 17% flow at 70% of its full opening.
Its the combination of the postal worker and the laid back surfer dude which gives stable control.
A coil designed for a 40 or 50 degree delta t has a more linearized performance and thus requires a different valve.
The Cv tells us how much pressure drop the valve experiences at a given flow rate.
How much pressure drop should the valve experience is the million dollar question.
To have controllability over a system, the control valve should experience at least 30% to 50% of the pressure losses in the circuit it is controlling. The ratio of the head losses in the valve in comparison to the head losses in the circuit is called Valve Authority.
A valve having no authority, no controllability, is too big. Too big is represented by the Cv. If the Cv is too large it means the head losses through it are less than 30% of the circuit losses. It also tells us that in small loads it will get confused not knowing whether to open or close. (which is most of the time for over sized valves)
When the proper Cv is selected the valve has controllability, ie: it is operating in the mid range of its stroke capable of opening up for greater flow or closing for less flow.
If a valve is selected with a small Cv it will have greater authority but it also significantly increases the head losses in the circuit and thus the horsepower of the circulator.
If the right Cv cant be found from the manufacturers data sheets then a balancing valve is required. Its the combination of the head loss through the control valve plus the balancing valve which creates the right conditions for controllability.
Finally a few last things to consider:
Zone valves ARE NOT control valves.
Valve leakage (see manufacturers data sheet) can have a negative impact on system stability. Some valves are simply not designed for fan/coil applications. (ie: rotary/shoe types)
On/off valves (zone valves) on a postal performing heat terminal unit tosses the whole concept of valve authority out the window one may as well put in gate valves.
The very reason why control manufacturers can take a single valve diameter but make it available with different Cvs and different personalities is because they understand marring valves to coils is a 'psychological' matching process...and is not for the amateur or those who like to use rules of thumb its a engineering design process no different than selecting a heat exchanger, circulator or boiler.
The wrong valve creates inefficiencies and temperature instabilities.
More importantly, inefficient systems with poor control create mad customers which tell two friends who tell their two friends who tell a few women and before ya know it the whole world knows how bad the system is all because of one oversized, incorrectly selected silly valve.0 -
Some comics for ya...
0 -
Over-dose
I think that Robert over-dosed on writings by Pedijean early in life. He knows way to much about valve authority for it to be healthy. Seriously though, this is what it is all about. You need to get the right valve for the application. Look forward to talking with you.
Tim D.0 -
3-way valves
are a particular problem. If using manual balance valves, it is necessary to put in two balance valves - one in the return from the coil and one in the line to the bypass to the 3-way valve. Or, you can put one automatic flow limiting valve (Griswold) in the return from the coil.
Properly selecting control valves is not that difficult if you have the right information, but I find that most modulating control valves are selected based on rules of thumb and wind up being over-sized. If the coil is also over-sized, the coil/control valve combination will not be able to provide stable control no matter what kind of control horsepower exists upstream.
If the system is constant flow (all 3-way valves) and is piped reverse-return, selecting a control valve with a head loss roughly equal to the head loss through the coil will usually provide adequate valve authority.0 -
Nice, RB
that's a post all should print and keep! Thanks for taking it to that level. It really notches up the level of info and expertise here, to be able to grasp that info.
I'll put you down for "best post of the month" club. Again
Thanks!
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I agree...
Tim knows I have this thing about control valves and balancing...got it from Professor RP himself. ( I think Jerry got rubbed by RP as well) RP is still alive and living in Belgium - a legend in the world of controls.
Jerry is right about the three way valve being a particular problem manufacturers offer them with ports having either the same (symmetric) or different (asymmetric) personalities and are designed as mixing (constant flow two inlets one outlet) or diverting (variable flow one inlet two outlets) devices.
and now you know one more reason why over 50% of building occupants are unhappy with their systems wrong valves - wrong combination of personalities- installed backwards but I digress .(see upcoming article in The News Designing for Failure Thanks to John Hall and Dan Holohan).
Since we control flow by controlling pressure and control pressure by the system design and equipment we need to understand where to place either automatic or manual balancing valves.
Some additional comments:
In constant flow (mixing) secondary applications with negligible influence from the primary circulator, the need for a balancing valve in the bypass line is questionable. However if the primary circulator has significant influence on the secondary side ( ie: the circs are in series when the valve is open) then a balancing valve should be placed between the primary return and the tee fitting connecting the bypass line to the three way valve. A balancing valve in the bypass line is required if its possible to have back pressure created by other three way valves configured as mixing devices but connected directly to a common primary network the automatic (Griswold) balancing device is definitely a nice product to have in the tool belt for applications where there is interconnectivity between primary and secondary loops.
In a variable flow (diverting) secondary applications with 100% influence from the primary circulator, a balancing valve in the bypass line is required and should experience the same head loss as the coil circuit. In this manner the bypass valve is in parallel with the coil and the circulator sees the same head loss whether the valve is open or closed.
In all cases there should be a balancing valve in series with the coil.
One of the major things to consider, especially in light of Mike Lundstrom question, is when it comes to control valves, pumps and comfort controls, its best to deal with a firm which understands the equipment, application and assembly. (It applies to 2, 3 and 4 way valves or injection pumps or manual or automatic balancing valves there are no short cuts!)
As I have said before control contracting is not pipe fitting anymore than a cabinet maker is a carpenter. They may be touching the same materials but what they do with it is two different games.
0 -
Wow!!
So much to know...so little time. Great post. It's all in the details.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Total Hydronic Balancing
By RP is the most informative piece ever written on this subject. There are very few copies in circulation so if you have one it is a treasure. If you have one that you don't want call me, PLEASE!
Tim D.0 -
I have a nice
piece that Tour Anderson put out years ago about hydronic balancing. A thick paper high gloss piece very pro photos and all.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Do you know where I could get a copy of such material?0 -
Is it a candidate for the library?
0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements