Pressure Reducer, & tankless: Expansion Tank?
to have one put in . Pressure reducers usually do not let water flow through them backwards , so a good buildup of pressure will kick the relief valve open . Hey Phil , is this the job you were talking about a few weeks ago ?
0
Comments
-
Pressure Reducer, & tankless: Expansion Tank?
Gonna put a whole house pressure reducing valve on M.I.L. house (street pressure is more than 125 psi). The gas fired boiler has a 4 gpm tankless coil in it.
Does this require an expansion tank?
What size?
There will be about 8 feet of 1/2" copper from the whole house reducer to the tankless coil.
Phil0 -
expansion tank
yes it does if you have a backflo preventer
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Expansion tank
For tankless coils we use a watts 150A water hammer arrester it is plenty big enough for the small volume contained in a tankless coil.
John0 -
Yep
Same job, Ron. I knew/know that with a water heater tank you need an expansion tank. I just wasn't so sure for a tankless coil.
Phil0 -
hammer arrester
Thanks John, for that tip. Do you have a favorite whole house pressure reducer? (Someone had recommended one a few weeks ago, but I mismember and cannot find that thread here. I didn't mark it.)
0 -
Reducing valve
> Thanks John, for that tip. Do you have a
> favorite whole house pressure reducer? (Someone
> had recommended one a few weeks ago, but I
> mismember and cannot find that thread here. I
> didn't mark it.)
0 -
Reducing valve
I use the Watts U5B
John0 -
Just make sure you use a potable water expansion tank...
FYI: every water heater doesn't need a tank, only homes with PRV's, like stated above, the act like check vavles and don't allow expansion back into the street water line0 -
I was just talking to a
serviceman buddy of mine and he told me they keep going back on new boiler installs with a coil . The domestic relief valves keep popping , even on the highest setting . I don't know if each home had a backflow preventer or a pressure reducer . Would those little white Amtrol Mini-trols work good for a coil and excess pressure ?0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements