why would steam radiator split?
Jim Miller
Member Posts: 10
job yesterday - complaint of radiators leaking - found 2 with end section having approx 4" vertical split - it is one pipe steam, 2psi......? what happended?
0
Comments
-
sounds like it froze. Ask HO if they were away? one maybe, but two? sounds fishy0 -
I thought about freezing
but the heat has been on continuously, besides the fact that a steam radiator should not have water in it anyway..........also, the way the venting is (no main vents) the radiators hardly ever heat all the way across, so the end section, the ones that split, hardly ever get hot, so I don't see it being heat stress related.........the system is very dirty - could that be it?0 -
\"Condensate Grooving\"
You have an acid condensate problem. Without proper main vents, CO2 in the air combines with the steam to form a mild carbonic acid. The rads didn't freeze, they were eaten away from the inside. At some point, this got to those end sections. I'm not sure why the end opposite the steam inlet failed first though- maybe it never really dried out in that area?
Dan covers this in Lost Art, in the chapter on Venting.
Measure the length and diameter of the steam mains and we'll tell you what vents they need.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
thanks - will be back there on Monday -
'preciate the input
Jim0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 65 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements