why would steam radiator split?

Jim Miller
Jim Miller Member Posts: 10
job yesterday - complaint of radiators leaking - found 2 with end section having approx 4" vertical split - it is one pipe steam, 2psi......? what happended?

Comments

  • Robert O'Connor_7
    Robert O'Connor_7 Member Posts: 688


    sounds like it froze. Ask HO if they were away? one maybe, but two? sounds fishy
  • Jim Miller
    Jim Miller Member Posts: 10
    I thought about freezing

    but the heat has been on continuously, besides the fact that a steam radiator should not have water in it anyway..........also, the way the venting is (no main vents) the radiators hardly ever heat all the way across, so the end section, the ones that split, hardly ever get hot, so I don't see it being heat stress related.........the system is very dirty - could that be it?
  • Steamhead
    Steamhead Member Posts: 16,796
    \"Condensate Grooving\"

    You have an acid condensate problem. Without proper main vents, CO2 in the air combines with the steam to form a mild carbonic acid. The rads didn't freeze, they were eaten away from the inside. At some point, this got to those end sections. I'm not sure why the end opposite the steam inlet failed first though- maybe it never really dried out in that area?

    Dan covers this in Lost Art, in the chapter on Venting.

    Measure the length and diameter of the steam mains and we'll tell you what vents they need.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Jim Miller
    Jim Miller Member Posts: 10


    thanks - will be back there on Monday -
    'preciate the input

    Jim
This discussion has been closed.