Yes you do
That's probably a "Circuit" system where one main wraps around the basement. 80 feet of 3-inch pipe contains 4.24 cubic feet of air. Technically this is within the capacity of a single Gorton #2 vent (5.5 cubic feet per minute) but I'd use two of these vents, since a long pipe like that has more internal resistance than two shorter ones handling the same load.
If you can't find Gortons in your area, call Gorton at 908-276-1323 and tell them I sent you. They will sell direct to you if no one in your area handles their gear.
The old boiler probably produced steam at a slower rate than the new one. That's why they could get away with smaller vents. New boilers make lots of steam quickly, and need more venting capacity.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Is there a way to get away with replaceing the single vent I have now?? I hate paying to have more asbestos removed but I want to make it right. where would you suggest the placement of the second vent be. you are correct the main wraps arround the basement in a large square.0 -
I could be wrong but....
if you add in a tee & a 90 at the same spot this will give you the spot. Just don't bullhead the tee...see what others say...kpc0 -
Say Steamhead and Dave...
Two thoughts..... is your steam travel time for warm or cold pipes? If the pipes are cold its bond to be slower since the steam needs to warm up the pipes as it goes. And second, maybe larger vents aren't needed. Remember vent the mains quickly is only part one of master venting, part two is vent the radiators slowly. If the rads vent too quickly, the steam is going to head for the rads before it gets to the end of the system. A few Gorton D's , or a few more adjustable vents set to full open are going to out vent even 2 Gorton 2's and throw the system out of balance. I think there was a reason the old Hofmman 40's were so slow to vent... it allowed the steam to favor the main at low steam pressures and once pressure built some in the system after the main vents closed, venting began to occur much more quickly at the rads.
Boilerpro0 -
My radiator vents are adjustable, I believe my vents on the second floor are wide open. what is the best stratagie for setting these vents?????0 -
Does this look like its set high???0 -
It's set over 5 PSI
> Does this look like its set high???
0 -
It's set over 5 PSI
It looks a little high, about 3 times too much for what you need, and about twice what the control can be set to on the low end and still work properly.
Noel0 -
could this contribute to my problem with the hissing radiators?????? can I just adjust down ?????0 -
It depends...
On the size of the radiator, type of radiator, the heat loss of the room, and the size of the riser. The only place I know to find sizing data for radiator vents is in the Deadman's Steam school workbook. Steamhead researched this info. Look over at books and more to purchase this info. Generally, with my limited steam knowledge, I don't open the vents more than about a third (a 3 out 10). Oh course if you have huge column style radiators that changes things. It all depends. This is where a good steam professional really helps. Experience and intuition play a big role here, besides doing the homework.
Boilerpro0 -
Installing Main Vents
Just pipe a tee onto the existing vent connection as Kevin says, and an elbow that will make the second vent stand straight up. And turn that pressuretrol down! Five pounds is way too high. Turn the screw on top counterclockwise so the pointer is at trhe bottom of the scale. Then TURN THE POWER OFF, remove the cover and turn the little white wheel inside so the number 1 points toward the front of the control. Replace the coverand turn the power on. The control will now stop the burner at 1.5 PSI and restart it at 1/2 PSI.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Is this the type of set up your talking about0 -
Exactly
I have a bunch of these vent manifolds out there and they work great.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Im thinking this is still a problem too. This is after four flushes by the contractor. my manual doesnt really cover how to flush the boiler. (weil-mclain EG 55). what is the proper procedure???0 -
Here you go
from the W-M EG/EGH manual.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I installed a single Gorton #2 vent in my main, I still have the hissing radiators. my guestion is will a second Gorton # 2 make a big dif. also after re examination it looks like my mains are 2in./ 80 ft. I was thinking maybe my radiator valves are dirty after firing up the new boiler. I was thinking of removing them and cleaning them in vineger. any suggestions ?????0 -
It will help
since more air will now go out the second Gorton instead of thru the radiator vents.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Gortons are in through out the house and I have 2 #2's on the main. still getting hissing and panting. I plan to do a flush, any other ideas????0 -
That's your next step
make sure you follow Weil-McLain's instructions to the letter! That boiler has gaskets between the sections and you don't want to ruin them.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements