Big motorized steam valve
Art Pittaway
Member Posts: 230
if a globe style valve is located in a horizontal run it will present a dam in the pipe that will hold condensate back. If it is installed that way without a trap or way to drain condensate you will have hammer. If the valve is installed close to a riser it can drain back into the main. Consider that even steam in a vapor system has velocity and will move the condensate along the piping to a point where it will have to be drained or will cause damage. Once again, it's a steam system and you have three fluids to deal with, steam, condensate and air/non-condensables. Miss one and you have problems.
Art
Art
Big valve...
I have a nasty feeling that I need a 3", preferably threaded, motorized steam valve (very low pressure -- so must have VERY low pressure drop!). I have 24 v control power available...
Checked State Supply; the biggest they have in motorized is 2" (Honeywell).
Any suggestions, guys?
Jamie HallBr. Jamie, osb
Is it possible
to repair the existing one? What is there now? What went wrong with it?
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Consulting0 -
Steam Valve
Check Invensys part# VB-9213-03-5-p, you can attach whatever
actuator you need, pneumatic or electric.
http://www.invensysibs.com/catalog/pdfs/2wygrtrn.pdf
Good luck, Steve0 -
3\" valve
Honeywell part # V5011A1767 you just need to select the actuator and thermostat or room control for the job.
3\" valve
put in a 4\" one last year, Jamie
Honeywell..Call Bill Wolfe @ the New Jersey office...he's the best and he helped me. Mad Dog
- 86.5K THE MAIN WALL
- 53 Biomass
- 94 Chimneys & Flues
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 41 Industry Classes
- 48 Job Opportunities
