pressuretrol problem?
Steven_2
Member Posts: 2
You were absolutely correct. Thank you. The pig tail was completely obstructed. Not even a breeze of air would pass when using compressed air on one end. It took about an hour of coat hanger work, hammer and propane torch to clear it out. I do not understand how the system could have been woring at all. Many thanks again,
Steven
Steven
0
Comments
-
pressuretrol problem?
My oil burner does not repond for a call for heat unless I raise the cut-in setting to above 1 psi (it is set at 0.5 psi) or raise the differential from 1 (where it is now set) to 5. Once the burner kicks on, I then readjust either setting back to baseline (the burner keeps running). Does this mean tht the pressuretrol needs replacing or could it be telling me something. (its a one pipe steam system if that is relevant)
Thanks much for any info0 -
pressuretrol problem
Check the pigtail pipe under the pressuretrol. Sounds like it's plugged. It will let pressure build and trip the switch but acts like a check valve and won't let the pressure back out. Pull it apart and clean it. If it's steel pipe, replace it with a brass one....
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements