I'm starting a small radiant job on Monday and the heated space is about 60 feet (one way) from the boiler. Do you guys usually keep your mixing valves @ the board or should I put it in the room. (The only problem w/ that is it will take up more space then just the two manifolds)

Thanks,
Jamie

Comments

  • heatboy
    heatboy Member Posts: 1,468
    Options
    You will have to move.........

    the pump also, Jamie, if you put the mixing valve near the manifold. That means pulling wire and taking up even more room.

    hb

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"

    There was an error rendering this rich post.

  • Josh M.
    Josh M. Member Posts: 360
    Options


    Not to mention it will be more difficult to do repairs in a finished room as oposed to a mechanical room or garage. I always just run pipe back to the boiler room. It has saved my company alot of money in the long run...
  • hot_rod
    hot_rod Member Posts: 22,200
    Options
    Insulate the

    supply and return to the manifols, 60 feet isn't to far.