Water conductivity for probe type lwco (steam)

Options
9000.

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=268&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>

Comments

  • Mike Lampkin_2
    Mike Lampkin_2 Member Posts: 124
    Options
    Water resistance

    Anyone know what the proper resistance should be for the
    water in a steam boiler using a PS-802 (McDonnell&Miller)
    probe type lwco? Instructions mention that conductive liquid
    is required. Would it be better to use a float type lwco in
    a steam boiler, rather than the probe type?
    Thanks for now, Mike Lampkin
  • Al Letellier
    Al Letellier Member Posts: 781
    Options
    water conductivity

    Mike, water is a conductive liquid. Probe/electronic LWCO's work great and are less troublesome from a maintenance standpoint. Just make sure you make cleaning the probe annually part of the boiler service tasking. They do get dirty and can fail if too much crud gets built up on the probe.