Need help with sound problem
Steven
Member Posts: 3
Hello,
I have a three zone, hot water baseboard radiant heating system in my house that has performed great. Recently, however, I had to replace the Bell&Gossett 100 series pump.
1. After installing the pump, I opened the cold water valve and completely flushed each zone using "new" water (with the pump and boiler turned off).
2. I then cycled through each zone with the pump and boiler turned on. All zones worked and I got heat!
3. Now each zone makes a running water sound -- there's no hammer or banging, more like a babbling brook. Before the pump replacement, there was no pipe noise.
4. I tried to remove air at each bleed-off valve on the registers, but it didn't seem like much air came out and it didn't seem to make much of a difference.
The noise isn't "terrible" but I'd like to get it back to slient. I have a single air-scrubber valve on the system, will this eventually remove the excess air? Is it air that's most likely making the sound? If so, how long should it take to expel?
I would appreciate any advice/comments.
Steven (Colorado)
I have a three zone, hot water baseboard radiant heating system in my house that has performed great. Recently, however, I had to replace the Bell&Gossett 100 series pump.
1. After installing the pump, I opened the cold water valve and completely flushed each zone using "new" water (with the pump and boiler turned off).
2. I then cycled through each zone with the pump and boiler turned on. All zones worked and I got heat!
3. Now each zone makes a running water sound -- there's no hammer or banging, more like a babbling brook. Before the pump replacement, there was no pipe noise.
4. I tried to remove air at each bleed-off valve on the registers, but it didn't seem like much air came out and it didn't seem to make much of a difference.
The noise isn't "terrible" but I'd like to get it back to slient. I have a single air-scrubber valve on the system, will this eventually remove the excess air? Is it air that's most likely making the sound? If so, how long should it take to expel?
I would appreciate any advice/comments.
Steven (Colorado)
0
Comments
-
Need help with sound problem
Hello,
I have a three zone, hot water baseboard radiant heating system in my house that has performed great. Recently, however, I had to replace the Bell&Gossett 100 series pump.
1. After installing the pump, I opened the cold water inlet valve and completely flushed each zone using "new" water (with the pump and boiler turned off).
2. I then cycled through each zone with the pump and boiler turned on. All zones worked and I got heat!
3. Now each zone makes a running water sound -- there's no hammer or banging, more like a babbling brook. Before the pump replacement, there was no pipe noise.
4. I tried to remove air at each bleed-off valve on the registers, but it didn't seem like much air came out and it didn't seem to make much of a difference.
The noise isn't "terrible" but I'd like to get it back to slient. I have a single air-scrubber valve on the system, will this eventually remove the excess air? Is it air that's most likely making the sound? If so, how long should it take to expel?
I would appreciate any advice/comments.
Steven (Colorado)0 -
The babbling brook
noise you are hearing is air indeed. You need to purge the system some more. Can take 1/2 hour or more per zone. Use a hose and put end in a 5 gal. bucket(this will let you see air )PS. might have to do this more than once Hope this helps John@Reliable0 -
Thanks, John
John,
Thanks for the reply. That's sort of what I figured.
Steven.0 -
Air
I had the same problem with my house. I really worked at purging this system. I really woorked at it. Finally I put a Spiro-vent on the system and that was the end of the babbling brook. I had heard they were good but was stunned and amazed at the difference.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements