The right way to connect a C wire?
I've got a Nest thermostat hooked up to a Weil-McLain boiler now. (I got the Nest for free and only use it for scheduling and sometimes remote control, not the smarts, so it works fine here.) The Nest's C wire is connected to ground. It's been happily steaming for years.
I'm getting a new boiler tomorrow. I could just wire it the same way, but I'm wondering if there's a right way to do it.
I would like for the thermostat to always be powered as long as the boiler itself has power from the mains. In other words, I would like the low water cut-off to not cut power to the thermostat. Of course, I would like the boiler to ignore the thermostat when LWCO is active.
On the Nest, R goes to G on the boiler, W1 goes to Y on the boiler, and C goes to C on the boiler, which is just ground.
I also have an indirect water heater. There's a Taco SR501 controller that handles it. TT on the Taco is connected to the temperature probe in the tank. On the 120 VAC side, N/O and N go to the circulator pump. On the 24 VAC side, N/O goes to G on the boiler and COM goes through a second temperature probe on the pump pump and then to Y on the boiler.
I believe what happens is:
- Temperature in house drops below 70 F, Nest connects its R and W1, turning on boiler.
- Temperature in water heater drops below 140 F, Taco connects its 120 VAC N/O and N, turning on pump. It also connects it's 24 VAC N/O and COM, which turns turn on the boiler if the boiler is under 180 F.
The Taco setup allows the pump to run even if the low water cut-off has tripped. This is because the Taco is powered from mains, so TT always has power, and the 120 VAC N/O and N to the pump can always supply power when called on. I tested this just now, and the pumped turn on when the LWCO was active. Is this expected, or should it be wired differently? On one hand, you probably want to get keeping making domestic hot water if the boiler is a little low temporarily. On the other hand, if the boiler is totally empty, I assume you'll burn out the pump if you run it.
When the LWCO is active, the Nest loses power. This is because power flows through the LWCO to G on the boiler, to R on the Nest, to C on the Nest, and back to C on the boiler. When the LWCO is active, G is dead, so the Nest loses power. That's what I want to avoid.
(By the way, what happens on a high pressure? Will the Nest also lose power?)
Is it possible to keep the Nest alive during LWCO? I heard about using separate transformers and relays in other threads here but don't know enough to confidently talk about it with the plumber and/or electrician tomorrow. Is there a single product that can do this? What should I ask for tomorrow to get this done properly?
Any installer worth his salt should be able to hook it up properly. I’m not a Nest guy but that’s another matter.
If you know what boiler you're getting go on line and find the manual and post the wiring diagram here. I have a diagram with a separate transformer and relay attached. There is more ways than one to do this sometimes.
Others will comment but adding another transformer and a relay will cost you $50 in parts and is foolproof.
You don't say weather the boiler is HW or steam. i will guess HW.
If you use a relay and transformer like my diagram the Nest will have power 100% of the time no matter what the boiler, lo water cut off or pressurecontrol are doing. The safeties, lo water, pressure control , aqustat, roll out switch whatever you have should shut down the burner only and theave the circulators running.
Take a look at your wiring diagram, @saikosis. Pick up R from the R terminal marked on the transformer (left diagram). Pick up C from the C termianl or any convenient clean ground. Lift the wire to the low water cutoff from the R teminal on the trabsfomer and splice that wire to the wire from W on the thermostat. The problem with your current wiring is that the thermostat is wired in parallel with the LWCO — which means that the LWCO can't cut off the boiler if the thermostat is calling.
This is very dangerous!
Now if the Taco is actually supplying 24 VAC across N/O and Com, you have been VERY lucky. If N/O and Com are actually dry contacts (unpowered) yoo can connect the Taco N/O and Com to the splice you made for W from the thermostat going to the damper connector. Otherwise you will need a relay with the coil powered by the Taco and the normally open contacts as above.
The various safeties — including the LWCO — must be operational at all times that the burner is enabled.
@Jamie Hall, are you warning about my current wiring or a hypothetical future wiring? I apologize if I misunderstood your post.
Except for the C wire, the current wiring has been in place since the boiler was installed. The C wire was connected to ground after the install.
The aquastats for the water heater and boiler are Honeywell L4080B1352.
Here is what I have for the Nest:
- R → LWCO → G → Nest R → Nest W1 → Y → …
- R → LWCO → G → Nest R → Nest C → ground
#1 should be standard. It lets Nest call for heat.
#2 is the extra bit that gives Nest power.
However, both heat and power are controlled by the LWCO. The LWCO disconnects R from G, disconnecting the Nest entirely. I have tested this. When the LWCO trips, the boiler turns off and the Nest loses power.
Here is what I have for the Taco:
- Taco R → tank aquastat bottom → tank aquastat top → Taco W
- R → LWCO → G → Taco N/O → Taco COM → boiler aquastat top → boiler aquastat bottom → Y → …
#1 wakes up the Taco when the temperature in the indirect water heater drops below 140 F. It turns the pump on through the 120 VAC side.
#2 lets the Taco call for heat, but only if the boiler water temperature is below 180 F, thanks to the boiler probe in the circuit.
Like before, the heat call is controlled by the LWCO. The Taco can run the pump with low water, but it can't call for heat.
The Nest and Taco are in parallel with each other, but both are in series with the LWCO. Is there something wrong with this setup?
—You said, "Lift the wire to the low water cutoff from the R teminal on the trabsfomer and splice that wire to the wire from W on the thermostat. The problem with your current wiring is that the thermostat is wired in parallel with the LWCO — which means that the LWCO can't cut off the boiler if the thermostat is calling." This is where I got confused.
I think you're describing R → Nest R → Nest W1 → LWCO → G → Y → …
That puts the Nest and LWCO in series. I think that would be safe.
- Heat call with sufficient water: circuit complete, boiler fires.
- Heat call with low water: circuit broken by LWCO, boiler does not fire.
- No heat call with sufficient water: circuit broken by Nest, boiler does not fire.
- No heat call with low water: circuit broken by both, boiler does not fire.
Right?
However, that omits my Taco. I don't want it in series with the Nest because that means both would have to call for heat to turn the boiler on.
Right now, my Nest and Taco are in parallel with each other after the LWCO. If I put them in parallel before the LWCO, I think it would work. Being in parallel with each other, either could still call for heat independently. Being in series with the LWCO, the LWCO could disconnect them from the burners. Being before the LWCO, the LWCO would not disconnect them from power. All of the loads may warrant dedicated transformer, but I think it would work in theory.