New Steam Boiler Setup Critique
Hi everyone.
I recently had a plumber install a 125 BTU natural gas steam boiler. Please rate the install and piping, cause if there is something serious that needs to be changed, then I can have them come back and change it. Please let me know if you need more additional pictures. I have skimmed the boiler myself for about 9 hours but I still need to do another couple of hours. I’m hearing water boiling in the 2 radiators above the boiler (1st floor and second floor). And when the boiler turns on and starts boiling water the radiator the second floor radiator hisses the entire time, until the boiler cycles off.
    mattmia2 Posts: 18,536
    does the hot water loop have a bypass? it needs a bypass to temper the water entering the pump when the boiler is steaming to keep it from cavitating and possibly to keep it from flashing to steam at the top of the loop.
    edited November 29
    also, can we see the controls with the front cover off? there should be an aquastat for the hot water loop somewhere
    you can't hand a piece of romex in mid air to power the hot ware circulator like that, it needs to be in conduit or armored cable.
    edited November 29
    so where are the controls for that hot water loop? there should be a relay for the circulator and an aquasat to keep the boiler from steaming when only the hot water loop is calling.
    i'm also not sure what is going on with that tee above the boiler. it looks like either there is a second main in the ceiling or a riser to the upper floors there and that isn't right for either of those cases.
    ethicalpaul Posts: 9,124
    That's more time skimming than you should need. Did you put washing soda or tsp substitute into the boiler for its first boil?
  • I’ve heard that some people need to skim their new boilers for around 15-20 hours
    EBEBRATT-Ed Posts: 21,456
    I have never had to skim a boiler for more than 1 hour. And that was commercial boilers a lot larger than yours. I always used washing soda or TSP.
    Circ pump is not supposed to be mounted with the motor pointing up.
    Do you have any main vents on the steam mains?
    With a new boiler I would have included new vents but others may not agree.
  • Steve214
    Steve214 Posts: 39
    How many cans of pipe dope did they use??? I’m sorry, but that’s a not a good install.
  • bburd
    bburd Posts: 1,353
    edited 2:08AM
    It is piped in black steel according to the manual, as far as I can see. It's a far better job than most HVAC contractors do with small steam systems these days.
    That said, the questions about the hot water loop are valid.
    Bburd