New Boiler, Unbalanced Mains
My single pipe system has two mains - one that runs the front of house and the other that runs the rear of the house. Each is about 40 feet long; the rear is a few feet longer. Each main is vented with a Gorton 1.
Back in October, I replaced my oversized Utica that was piped wrong and had developed a leak above the water line. I ran the new boiler for a few weeks in October to clean and skim it, and things were balanced and good. Then it did not run for a few weeks as the weather was mild. It was after this period of not running that the mains' venting went off the rails.
The front main now vents way faster than the rear to the point that the rear does not fully vent and radiators off the rear do not heat. The front radiators all fill with steam. This was never an issue. Both mains would vent equally and I had the radiators well balanced using mostly Maid o Mist 4 and 5 vents. I have tested the main vents and found no issue. I even switched the front one to the rear and vice versa. I also tested by removing the vent from the rear main and running it open. It made little to no difference.
When the venting issue started I noticed the boiler pressure would bounce between .25 psi and .5 psi as soon as the header would fill with steam. Prior to this, I don't recall seeing a pressure reading on the new boiler. The old Utica would build pressure on long calls for heat. Also, I could hear a whoosh of air from the front main vent when steam hit the header. The rear main vent and the radiator vents off the rear just kind of puff puff with venting. Otherwise, the system is very quiet. The water level in the gauge glass drops about 1 to 1.5 inches when it starts producing steam. The low water cutoff is not triggered.
I'm grateful for any advice.
01_boiler.jpeg 02_boiler.jpeg 03_boiler.jpeg 04_rear_vent.jpeg 05_rear_return.jpeg 06_front_vent.jpeg 07_front_return.jpeg
    EBEBRATT-Ed Posts: 21,440
    Boiler looks piped right. Nice Job.
    First thing that comes to mind I wonder if when the mains were reconnected to the boiler if the pitch on the return may have been changed slightly casing a water pocket. The fact that the vents huffs and puffs kind of leads me in that direction. but you say the system is quiet which would not indicate a water pocket.
    Also make sure the vent connections can't trap water and slow the vent down. 45s may be better than 90s
    ethicalpaul Posts: 9,122
    Did you verify the vent on the main that does heat is allowing air to escape? Remove it, hold it upright and blow into it to check.
    With your radiators having 4 & 5 vents, there’s nothing else that would keep both mains from filling
  • patrykrebisz
    patrykrebisz Posts: 181
    edited November 27
    You have same size pipes feeding front and back. This means that on cold start up (and without insulation every call for heat is cold start up), steam favors the pipe closes to the raiser (in your case the front pipe).
    This is what theory says and it seems the practice proves it with your system.
    The solution:
    1. Insulate your pipes (with warm pipes the steam will go to both pipes at the same time).
    2. Since with cold start steam will always favour the front main pipe, you might want to increase the back main vent.
  • neilc
    neilc Posts: 3,223
    either speed up the rear, drill it? make the rear less restrictive, 2 45s instead of the 2 90s would flow better,
    or slow the front, tape? and a pin?
    your steam is contained, and building pressure, better, instead of weakly and going up the chimney also,
    known to beat dead horses
  • saias
    saias Posts: 26
    @EBEBRATT-Ed I checked the pitch and it's ok. There's one section about 3ft that is level but that was the case before the new boiler.
    @ethicalpaul Yes, I tested the vents. No issues. Air escapes upright, and they close when upside down. I even ran it open, with no vent in the rear main. It did not seem any different. The vent bushing is only 1/4".
    @patrykrebisz I wondered if it would favor the first takeoff. But it did not do this with the old boiler and the new boiler ran pretty balanced for the first few weeks. I should insulate the mains, but also they were not insulated with the old boiler. It does not vent any better when it starts with hot pipes.
    @neilc I will try slowing the front to see if it makes a difference. I probably should be using Groton 2 for the length of mains. I would have to get the bushings out since they are only 1/4", and I would rather not take that on with heating season in full swing.
    Would a clogged return cause venting problems?
    edited November 27
    ok sorry for missing that info in your original post.
    I would not suspect the return.
    At this point I would guess the rear main is improperly pitched but it’s just guessing. Is there anywhere on that main where water would sit?
    I see Ed suggested this already and you said it’s ok but your description points to this
    109A_5 Posts: 4,852
    These two things is bother me
    " When the venting issue started I noticed the boiler pressure would bounce between .25 psi and .5 psi as soon as the header would fill with steam. "
    " The water level in the gauge glass drops about 1 to 1.5 inches when it starts producing steam. "
    I'm thinking you are not done skimming. After your first boiler run and skim more oil has settled on the boiler's water.
    It is throwing up water into the header and it ends up in or blocking (restricting) the rear main's steam flow.
    Steamhead
    edited 1:11AM
    If the vents are "panting" (as the op said) there is a slug of water somewhere