Scalding hot water

Options
kingsoverqueens
kingsoverqueens Posts: 7
edited 7:06PM in Domestic Hot Water

Hello forum, first post from a homeowner.

I have a 21 year old radiant heat system with 7 pumps that service heat, plus a primary pump that services the loop, and an injection pump that services the heating loop. There is also a pump for domestic hot water with water held in a 6 year old Weil McLain Series 2 water tank. There is also a separate pump for the basement baseboard. The pumps for the baseboard loop and the domestic hot water are connected to the boiler loop.

About a year ago I noticed heat coming from the baseboard when the primary pump was running to satisfy a call for heat in other zones and through trial and error concluded that the check valve or valves in the isolation valves were stuck open allowing water to run through that particular zone. Some vigorous manipulation of the isolation valves and gentle but firm taps with a hammer solved the problem.

Flash forward to two weeks ago when I noticed the domestic hot water was scaling hot and confirmed 180 degrees with my prob thermo. Just like before the primary pump was running and I could hear water running through the zone. Just like before a few taps with a hammer on the DHW isolation valves and some vigorous manipulation solved the the problem…until today and it's doing it again. Today however I didn't observe the primary pump running.

I'm noticing this happens earlier in the day when there hasn't been much of a call for hot water, and have read about "stacking." The temperature control is set for 110. I should point out that after correcting the check valve, the water was still 130 to 140 degrees.

Some recent repair history.

The water tank was replaced in 2020.

The expansion tank replaced in February 2026.

Both pressure relief valves for the boiler and hot water tank were replaced in July 2026.

The pressure reducing valve also replaced in July 2026.

I was very careful to not introduce air into the system and ran the loops so that air scrubbers could do their jobs.

I have 3 questions.

The first, should I flush out the boiler side of the domestic hot water tank to clear any sediment that might be gumming up the works? I know the water in the system is dirty but perhaps some street pressure might do the trick?

Second, is it possible that the water holding tank is being warmed through heat transfer from the hot water in the boiler loop? The inlet and outlet pipes are hot to the touch, I'd go as far as to say very hot, but I don't know the temp. Could that hot water transfer enough heat to the hot water tank, given enough time?

Third, should I replace the electric heating thermostatic control?

Thanks in advance!

Photos of the system:

Boiler loop in front, heating loop off to the right. The black (injection) pump serves the heating loop and the red pump serves the boiler loop. The baseboard pump I mentioned is to the left of the injection pump.

20261121_125637.jpg

Return loop from hot water tank outlet at bottom of tank to the boiler loop.

20261121_125535.jpg

Another view of the entire system with the DHW loop closest.

20260201_130817.jpg

DHW pump feeding inlet side (middle) of hot water tank.

20261121_125554.jpg

Pump

20261120_130939.jpg

Check Trol isolation valve.

20261121_125621.jpg