One zone still looks warm after the thermostats are satisfied

Options

I noticed one room was staying warmer than expected after the thermostats had stopped calling for heat.

I used a thermal camera to scan the accessible zone valves and nearby piping. Most of the zones had cooled down, but one valve and the pipe after it were still showing a warmer pattern.

That narrowed the problem from “why is the house still heating?” to one specific zone. I’m trying to work out whether I should start with the valve itself, the control wiring, or possible ghost flow.

Poll: What would you check first?

  • Zone valve not closing fully
  • End switch or relay still calling
  • Ghost flow through the zone
  • Circulator running longer than it should
  • Need the piping and control details first

Comments

  • hot_rod
    hot_rod Posts: 28,807

    need more info, including brand and model

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream