Velan bimetallic trap suitable for 2 pipe heating system?
Pumpguy
Pumpguy Posts: 814
edited 7:45PM in Strictly Steam
Attached is a data sheet showing a Velan bimetallic steam trap I recently saw on one of my customer's 2 pipe low pressure steam heating system.
I've never seen this trap used on the radiation of a conventional 2 pipe gravity drain steam heating system, or any other application for that matter.
My real concern is dealing with the air venting. It seems to me this trap would form a water seal and not allow free air venting.
This would be for use with a 1 PSI steam supply pressure, and gravity condensate drain down to a condensate return pump.
What are the group's thoughts? Are my concerns valid? Is this trap suitable for this application?
    Jamie Hall Posts: 28,018
    It appears that it would work — but it's clearly intended for use on process steam, or possibly an air handler. It will cause some condensate to be more or less permanently trapped in the radiator, if used that way.
    Why would one want it in place of a "normal" trap, I might ask?
  • Pumpguy
    Pumpguy Posts: 814
    edited 8:38PM
    Can't answer your question Jamie. I've just learned this trap is produced by a small company, local to the end user. I have a call in to their tech support but won't get any answers till tomorrow. Could be a local thing, maybe.
    This is installed in a 1930s industrial building. The boiler used to run 24/7 for an industrial process. Steam was tapped off through a PRV for building heat.
    These days boiler only runs intermittently for the process. So, when they need to heat the building, they need to bite the bullet and fire up the process boiler just to heat the building.
    Now, goal is to make their system as efficient as possible, so asking, is this a suitable trap for the job?