Arco 915 air separator with 3/4 steam trap

Options
robertm1976
robertm1976 Posts: 2
edited 5:41PM in Strictly Steam

hey there, I’m new here. I’m a tech with Reiner Group Inc in Northern New Jersey. I have been in the field for over 30 years but have only ever worked on 2 pipe steam systems 3 times. I have a bad arco 915 air separator and could use some help on getting this system running again. I was told to remove steam trap and install an antler manifold with multiple Gorton steam vents. Curious if anyone else has done this with success. Any help would be greatly appreciated. Here is a picture of the proposed solution as well as existing setup.

IMG_2995.jpeg

IMG_2996.jpeg

Comments

  • mattmia2
    mattmia2 Posts: 18,468

    what does the rest of the system look like? what trim is on the radiators? what controls are on the boiler? that looks like it might be to equalize the pressure between the mains and the returns. don't just start changing stuff until you understand how the system works(or was supposed to work before someone that didn't understand it started changing things).

  • robertm1976
    robertm1976 Posts: 2

    My apologies, I was not on the job site and unfortunately the technician took 4 pictures, the other one showing the 2 pipe radiator. I spoke with an older engineer who is familiar with these 100 year old systems. Of course replacing the air separator would be best, that is not an option because unfortunately it is no longer available. Was just wondering if anyone had heard of this as a solution. The issue is the system has only one air separator as seen in the picture, air is not being vented out, so all pipes are hot up to rads but the radiators and everything else downstream is cool. I will be going to look at the job myself next week to get a better idea. Like I said, I was only curious if anyone else had heard or seen this done as a solution.

  • mattmia2
    mattmia2 Posts: 18,468

    we need to know what they system is. it may be a vapor system. the problem with venting may be steam in the returns closing the vent and what will cause that will depend on the type of system.

  • Jamie Hall
    Jamie Hall Posts: 28,018

    It is very likely to have been a vapour system. In which case, yes you do need some sort of main vent ("air separator") and that old Arco is likely to be the best place for it.

    Your proposed fix may work quite well.

    HOWEVER.

    It is unlikely at best that that is the only problem. As others have asked, please let us know what the trim on the radiators is like. Also, what pressure control is used on the boiler, and what is it set to?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2