Balancing this new manifold

Options

7-zone Uponor with flow meters, fed by a Grundfos 15-58 Alpha

7 tstats for 7 zone valves, so the Alpha is staying on constant pressure mode.

At medium force (10ft), and all loops flowing, I was able to balance the garage loop flowing at 0.45gpm and the 6 house loops at 0.35 each. Total flow indicated on the Grundfos is 2.5gpm (resolution of 0.5) so they seem to agree.

Should that be considered reasonable flow, or should I step up the Grundfos to max force (15ft ?) and try to balance that ?

I was able to get that very long garage loop (300+ft) up to 0.75gpm using max force when I was chasing each loop solo to rid the air.

Is the penalty just electricity used ? The other zones would be throttled back quite a bit at 15ft pressure.

30+ yrs in telecom outside plant.
Currently in building maintenance.

Comments

  • bjohnhy
    bjohnhy Posts: 222
    edited 5:47AM

    Are you monitoring return temp (delta T) of each loop as you dial in the flow? A good goal would be Delta 10-20F depending on what your design calls for. I favor closer to 10F if your dialing the loops individually

  • Jamie Hall
    Jamie Hall Posts: 28,010

    Flow numbers are not what you are looking at. The question is is the space getting the heat you want?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • hot_rod
    hot_rod Posts: 28,791

    Higher flow rates give you more output, but also a more consistent floor temperature. So for residential comfort it is worth chasing a tighter ∆ than 20.

    In my mind go for the most flow with that Alpha, at only 44W is doesn't cost you much power.

    The RPA calculator suggests .6 gpm for 1/2 pex.

    .75 gpm in a 1/2, 300' loop looks like this for pump spec

    Screenshot 2026-11-18 at 8.02.34 AM.png

    For illustration purpose, here is how the loop temperature might look. Although these higher flows are not necessarily worth pumping to.

    1.48 gpm to get to a 12°∆ would be around 20', out of reach for that Alpha, but possible with the Alpha 26-99.

    Screenshot 2026-11-18 at 8.37.53 AM.png

    Bottom line IMO, crank the Alpha to speed 3.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Peter49
    Peter49 Posts: 7

    I'd check how the flow rates change when only one or two zones are calling for heat, as the circulator will see different resistance depending on which loops are open. If the garage loop is heating properly and the supply/return temperature difference looks reasonable, increasing the pump head might just waste electricity without improving performance.