Boiler not building pressure

Options

Hi all, my 100hp boiler fired up in high fire. It produces steam (2 pipe system in a 6fl building) but there is no pressure. There is nothing wrong with the gauge. This year I notice no air whistling out of the main air vents. They eventuality get hot but the radiators take too long to fill and the temp is barely 200 degrees. I also noticed that it isn't as hot in the boiler room while the boiler is on. Is it possible I need to have the fire tube cleaned (mostly use gas)? It hasn't been done in at least 4 years. Could I have scale build up on the tubes? Not sure what else can produce this condition

Comments

  • ScottSecor
    ScottSecor Posts: 1,083

    If the fire tubes have scale on the outside it will slow the boiler water from heating up.

    If the fire tubes have soot or some other debris on the inside they will slow the boiler water from heating up.

    Unless the tubes are in really bad shape, I do not think this is your problem. Has the burner been altered? Has anyone tuned the burner recently? Is the boiler combustion efficiency still the same as it was when last tested? Is the boiler stack temperature much higher than it was? This may indicate the boiler needs maintenance.

    Does the burner cycle, or does it run non-stop twenty four hours a day? If it does cycle, what control is making it? Is it the pressure control, outdoor reset, or some other device? I am guessing the boiler may not be running for long enough cycles, perhaps in an attempt to reduce fuel consumption?

  • pecmsg
    pecmsg Posts: 7,653

    what type of Building?

    When was the last time it was serviced?

  • Wvega123
    Wvega123 Posts: 28

    The burner was service recently and it appears to be working fine. The combustion test were the same as earlier this year. Earlier this year it would take 50-60 minutes to reach the cycle complete return temp. Now it runs for 90 minutes before the return temp starts to increase. It would take hours for the return temp to shut the cycle off.

  • pecmsg
    pecmsg Posts: 7,653

    combustion analysis #’s?

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,360

    Someone needs to re check the burner and walk the building. 2 pipe steam you probably have a condensate return pump or boiler feed tank. Check the vent pipe from the tank. it may be piped outside and could be blowing steam. When were your traps serviced last?

  • mattmia2
    mattmia2 Posts: 18,436

    is it losing water? is there a hole above the water line sending steam up the vent?

  • Steve214
    Steve214 Posts: 20

    Sounds like you’re steam cleaning the chimney. Does the top of chimney look like a locomotive when the boiler is running?

  • Wvega123
    Wvega123 Posts: 28

    Last burner results efficiency 83.4 gas 91.9 oil. There are no water issues. The level hasn't changed the last few weeks. There is no steam exiting vent above the return tank. Nothing unusual from the roof chimney. There are probably radiator traps that could be updated but since there is no steam reaching the traps or return line Im not worried about them.