Problem getting new baseboard loop hot on old gravity system with newer gas boiler
There was a 3ft and a 4ft baseboard heater added on to what I believe to be an old gravity boiler system with Cast iron radiators. There are 2 main supply lines that are 2" black pipe and 2 main return lines that are 2" black pipe. From the 2" mains it breaks off into 1-1/4" black pipe supplying the radiators and returning from the radiators. Looking at the boiler, the supply and return to the left go to the living room and the bedroom above the living room. Looking at the boiler the supply and return to the right go to the dining room then then to the two upstairs bedrooms ( a single 1-1/4" from the main tees somewhere in the wall and reduces to 1" pipe at the radiators upstairs) then lastly supply's the baseboard heaters which comes off of the main at 1-1/4" black pipe then reduces to 3/4" copper at the baseboard heaters (1 straight 3/4" pipe connecting both heaters through a wall). My question is, is there a better way for me to plumb all of this altogether? ( What gets supplied first what gets supplied last, which type of fittings are best where, out the pump on the supply side instead of return side, install an air separator etc.) Or is there a way I can just re plumb a manifold at the boiler with a 2nd circulator pump and zone control without short cycling the boiler? Or lastly, is there a way I can use balancing valves to solve the restriction problem (if there is one)? Or is there another solution that I am not seeing?
You will not get a copper tube w/alum fin baseboard to heat a room by connecting it to the pipes that used to feed a cast iron radiator. They work on different principles. The cast iron has slow flowing water that stays in the radiator for longer time frame. it moves thru the pipe slower than 0.5 gallons per minute (GPM).
The copper baseboard needs constant water flow of 1 to 4 GPM to maintain the heating needed.
With those two different radiator types you need separate thermostats connected to separate circulator pumps on separate zones.
3 -
anytime the zone output is lower thanthe boiler output, the boiler will short cycle
what size is the boiler, the output number!How many feet of fin tube?
You can somewhat predict the cycle lengths. On milder days the cycles will be more frequent
Living the hydronic dream0 -
Hey Ed, if I put the two baseboard heaters on their own zone with their own thermostat and circulator pump, how do I make sure the boiler doesn't short cycle?
And no the baseboard loops never worked it is about 8ft of aluminum fin and tube and the boiler output is 78,000 BTU input is 95,000 BTU. It has a Taco 007-F5 pump and the 8ft of baseboard is the last branch off of the main 2" supply pipe on the right side of the boiler and it reduces to 1-1/4" from the main 2" pipe then down to 3/4" copper just before the baseboard heaters.
8’ of baseboard is about 4k btus. On a 95k btu boiler, it’s gonna short cycle the boiler to death.
The best thing you can do is remove the baseboard and put a sufficiently sized cast iron radiator back in.
Bob Boan
I'd try having the baseboard zone on its own circulator controlled by a thermostat in that zone. However that zone simply cannot fire the boiler. There may be enough residual heat in the boiler to satisfy that zone from the activity of heating the rest of the house.
If not I would set something up so the boiler can only run once per call for heat from that zone. but that gets into more exotic control techniques.
One Pipe System0