Eg-75 header change
Hi there, I'm replacing failed 1-1/2” pipe for the loop and block. Should I take the time to make the header all 3” and move this reducing elbow to the vertical line as Weil McLain suggests? I plan on it but not knowing whether it will make of a difference is bothering me. Thanks in advance. I don’t want to dig further into it if it doesn’t need it due to time I don’t have to get this thing ready
Comments
-
If there is nothing wrong with the supply riser and the header (meets the manufacture's specifications) I would just correct the drip to the equalizer by removing reducer bushing. The pipe size reduction should be in the vertical piping not in the horizontal header.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
Yup, figured. Thanks for confirming trust my gut and do it right.