Water level problems

Options
Paul S_3
Paul S_3 Posts: 1,303
edited 1:38PM in Strictly Steam

Hey everyone, hope all is well.

We replaced a steam boiler last year, and I’m looking for some guidance on a recurring low-water issue. The original boiler was oversized by approximately 80 square feet EDR. The replacement is closely matched to the connected load of 938 square feet EDR, possibly slightly undersized. All the basement steam piping is insulated, and the system heats the home extremely well.

After approximately 20–30 minutes of continuous firing, the water level drops enough to trip the low-water cutoff. The default VXT feeder’s time delay allows the condensate to return before it adds water. After about five minutes, the water level recovers and the boiler resumes firing. The boiler heats the home extremely well even though it trips on low water.

I’ve skimmed the boiler multiple times and also cleaned it with a wand, but the issue persists. The wet returns were replaced approximately four years ago. I’m starting to wonder whether the replacement boiler needs a reservoir tank to provide additional water volume while waiting for condensate to return.

Some background on the system and installation

Two-pipe vapor system originally equipped with Haines Vento radiator traps and graduated radiator supply valves.

Radiators on the first and second floors. All radiator traps were replaced when the wet returns were replaced a few years ago.

Six ducted indirect heaters in the basement also serve the first floor. These sit approximately 2–3 feet above the boiler’s normal waterline.

Each indirect has a steam supply and an untrapped condensate drip into the wet return. The indirects are vented through crossover traps connected to a dry return above the heaters.

Vaporstat set to 10 ounces. The 0–3 psi gauge rarely shows any pressure.

Boiler piped with a 4-inch drop header.

Boiler water pH approximately 7.

How do i determine whether the boiler needs a reservoir tank or whether additional skimming and cleaning are necessary? Could the indirect heaters’ piping arrangement contribute to delayed condensate return?

Thanks for any guidance.

Paul

ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • JohnNY
    JohnNY Posts: 3,420

    You may already know this but problems that require some significant run time in the cycle to show up are generally pressure related or there is an oversizing issue that overwhelms the system as vents start to close. You seem confident in your EDR numbers though. An expensive way to (probably) fix this is to install a second vaporstat and a step-fired gas valve (it's probably already there in a boiler at that output) to create a 2-stage burner. Another quick experiment might be to plug off the two outer burner tubes and see how that affects system behavior.

    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • 109A_5
    109A_5 Posts: 4,740
    edited 2:17PM

    Does the water just slowly steam away or is the water line violent? Maybe this will give you some help.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • JohnNY
    JohnNY Posts: 3,420

    Has anyone ever successfully created that reservoir pipe that Weil-McLain has so casually included in their EG(H) piping diagrams for decades?

    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • 109A_5
    109A_5 Posts: 4,740
    edited 2:40PM

    There has been at least one post with a pipe type reservoir with welded on end-caps, not sure if it is actually pipe or some sort of steel tubing and I believe it was added to a peerless boiler.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    JohnNY
  • Paul S_3
    Paul S_3 Posts: 1,303

    @109A_5 it looks like it slowly steams away but the boiler is very wide. I hear the pressure controls shaking when I listen closely.

    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • 109A_5
    109A_5 Posts: 4,740

    @JohnNY, @JUGHNE posted this in another thread.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    JohnNY
  • STEAM DOCTOR
    STEAM DOCTOR Posts: 2,680

    Why not just leave things the way that they are? Building is heating properly. You effectively have a variation of the hydro level cycle guard

  • STEAM DOCTOR
    STEAM DOCTOR Posts: 2,680

    Did you check the gas pressure? Very often, the gas controls themselves are not set properly. Maybe it's over firing?

  • Paul S_3
    Paul S_3 Posts: 1,303
    edited 2:40PM

    @STEAM DOCTOR customer understands short cycling and system wear and we just installed it not even a year ago. I never caught this after we originally installed it. And I feel if i used a different water feeder like the McDonnell Miller. I would've got a flooded boiler service call because of the default time delay

    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • 109A_5
    109A_5 Posts: 4,740

    Assuming the old boiler did not have the same issue I wonder if the water capacity was similar between the old and the new boilers.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Paul S_3
    Paul S_3 Posts: 1,303

    @109A_5 the old boiler was a Utica about 25 years old. It was a lot taller than the weil mclain egh 105 that's there now but no where as wide