Have You Ever Made A Mistake?

Options

I installed this Viessmann Vitodens (172K BTU) in 1997; replaced an old Hydrotherm. In-slab radiant, ~4,000 [], 18' ceilings, floor to ceiling single pane glass windows. The house is suspended in mid air over a steep ravine. An architect's dream, a heating contractor's nightmare.

Back then, the max. temperature you could get from a Vitodens was 167℉. That year - 1997 - we had a particularly cold winter and the boiler just couldn't keep the house warm, even running at max. setpoint.

Luckily, we haven't had winters as severe, but the owners never called me back. They tore my stickers off the boiler and pump control module. Since then, the husband and wife died and the daughter has moved in. The boiler is still working even though there's been a lack of maintenance, but her insurance company is making her get a new one.

Imagine running that high a temperature water in the slab. Bare slab or tile mostly; carpet in the bedrooms.

0-10.jpg

0-11.jpg
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab
mniska

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,427

    Add supplemental baseboard?

    mattmia2
  • mattmia2
    mattmia2 Posts: 18,513

    or panel radiators or even hydroair.

  • mattmia2
    mattmia2 Posts: 18,513

    has the neutralizer dissolved all of the calcium?

    also not so common to have a neutralizer in 1997.

    everyone but the architect's nightmare.

  • kcopp
    kcopp Posts: 4,744

    Curious why the insurance company is requiring a replacement?

    How do you plan on rectifying the situation?

  • hot_rod
    hot_rod Posts: 28,856

    can you lower the load anyway? Spray foam below the home, blower door test?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    JohnNY
  • @EBEBRATT-Ed Baseboard wouldn't really look good. It's pretty fancy inside and installing the piping under the house would be difficult. You'd need some serious scaffolding. Some nice Runtal or equal rads would work.

    @mattmia2 We installed a few of those neutralizers back in the 90's. Sold along with the V. boiler. It actually doesn't need a neutralizer since it drains into the ravine. I'm sure there are some acid loving plants down there.

    @kcopp The insurance companies don't want to pay for any catastrophic damage done by old equipment. They also want a seismic valve on the gas line and a water monitor on the water service.

    @hot_rod The house could really do with some floor, wall and ceiling insulation along with new double glazed windows. It's just a question of money.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • So, you're doing the replacement/upgrade ?

    Isnt that the tops of trees seen down thru the support framing ?

    I get the idea of nature. I live in it too. As long as you cant see the neighbours house , and you have lawn, trees, birds, deer whatever… thats cool.

    But,, edge of a cliff ? Hard no from me lol.

    30+ yrs in telecom outside plant.
    Currently in building maintenance.
  • mattmia2
    mattmia2 Posts: 18,513

    i bet you could get a spacepak with a hot water coil in there somewhere.

  • There’s also a heat sucking atrium in the middle of the house.

    IMG_3012.jpeg
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    GGrossbjohnhyskyking1
  • bjohnhy
    bjohnhy Posts: 229

    "architect's dream, a heating contractor's nightmare"…… well said.

    What would you do differently if you could do it over?

    kcopp
  • I could have chosen a different boiler with a higher setpoint, but I don't like running radiant at such a high temperature. I believe the owners were warm 95% of the time.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • hot_rod
    hot_rod Posts: 28,856

    that house may not be a good candidate for radiant floor heat. You probably do not have enough floor sq footage to cover a assumed very high load? Has a load calc ever been done?

    The structure not the heating system is the problem 🤔

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Alan (California Radiant) ForbesSTEAM DOCTORskyking1
  • They could have tightened up on the tube spacing.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    bjohnhy
  • mattmia2
    mattmia2 Posts: 18,513

    how well is the underside of the floor insulated?

  • JohnNY
    JohnNY Posts: 3,424

    If you've ever got 9 or 10 hours to spare, I'll tell you of the mistakes I've made that immediately come to mind.

    I don't think is a mistake though.

    This problem was engineered into the home long before you got there.

    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    bjohnhyAlan (California Radiant) Forbes
  • DCContrarian
    DCContrarian Posts: 1,600

    If you didn't design the system and all you did was replace the boiler, I'm not sure it's your mistake. Do you even know if the old boiler was heating the space either?

    I go back to your signature tag, "Two btu per sq ft for degree difference for a slab." There's only so much you can get out of a slab before it becomes uncomfortable to walk on.

    bjohnhy
  • hot_rod
    hot_rod Posts: 28,856

    if the occupants are warm 95% of the time, it sounds like the system is adequate for design day condition? 5% of year at below design condition is is too cold inside?

    Probably calculate that atrium square footage counting the walls at R-3 since it is mostly glass.

    As @DCContrarian mentioned the floor at comfortable 82 surface is only going to get them 20- 25 btu/ sq ft depending on ambient temperature.

    I doubt, even in your climate that 20 btu heats that atrium?

    But, I don’t see any of this being on you?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • DCContrarian
    DCContrarian Posts: 1,600

    Design day is 99th percentile. 88 hours per year.

    At 95% of the time, that's 440 hours per year, or 18 days. That's a lot.

  • Alan (California Radiant) Forbes
    edited November 9

    I never forget an unhappy customer. Especially when all I can say is to insulate the house better. I should have recognized the difficulty and alerted the customer before doing the work.

    @mattmia2. Joists bays are exposed. i.e. no insualtion.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    GGross
  • mattmia2
    mattmia2 Posts: 18,513
    edited November 9

    since half the heat or more is going outside you could run the loops at a higher temp without the floor getting too hot.

    alternatively they could insulate it with a couple inches of foam and cover it in such a way that the joists are still exposed. as a bonus they would only be paying $3k a month to heat it instead of $6k.

    but if it look at what i did in 1997 when i had neither money nor experience…

    Alan (California Radiant) ForbesPC7060
  • hot_rod
    hot_rod Posts: 28,856

    but I don’t see you being the reason for their unhappiness?

    if they were uncomfortable for only 5% of the time as a result of the improvements you made. Chalk that up as a win.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Larry WeingartenAlan (California Radiant) Forbes
  • Grallert
    Grallert Posts: 1,258

    I don't think there's enough floor to heat the place. I've run into this twice. I designed a system for my sister. Beautiful post modern in New England, glass walls single pain. The design called for supplemental heat to meet the load. Husband said no to panels or cast iron. That was a cold house.

    Another one. Hills of western mass. An addition I didn't do but was called to look at. Same thing. not enough floor for an all glass cathedral ceiling. They wanted me to bring my assessment and go to court with them.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

    skyking1
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,067

    They are not mistakes, they are learning experiences. …and firing the guy that had the most experience on the job was the best thing for you Alan. Now you have all this experience to work with to solve the problem. Or you could walk away. You are in the catbird's seat now. But I'm sure you will do the right thing.

    I remember firing 4 different customers in my career. One I called a crook by using his own words about me against him and asked them to call one of my competitors. There are better crooks out there than I. LOL

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • breeze
    breeze Posts: 7

    you are a better man than me Alan. I would have let the guy freeze. Enjoyed the post and comments

    Alan (California Radiant) Forbes
  • Interesting. My Brother and SIL lives out in Northern California. There are a lot of houses built on the side of mountains. I don’t know how folks can do it lol. I would be terrified. Honestly, with such a small percentage of uncomfortable days, a wall hung electric space heater is the perfect solution for the little gap in comfort.

    Lifelong Michigander

    -Willie

    GGross
  • fastd
    fastd Posts: 20
    edited November 16

    Another architect's dream! Plug in some portable electric heaters when it gets to cold, and keep them in a closet out of sight when not needed.

  • Jack
    Jack Posts: 1,063

    have to say that I am impressed that the system has held up give the towering sub-structure. Excellent engineering and build to attain that. Rather than pushing the spec and comfort level that system that you know is doing 100% of what it can, to supplement this place adding a Rinnai DV wall furnace would likely have solved the temporary issue. I’ve done that many times over the years.

  • Steamhead
    Steamhead Posts: 19,030

    I had a similar situation many years ago. The owners of an old house wanted to turn the deck into a four-season room. They asked about radiant, but a heat-loss calc showed not enough floor area.

    The main house had one-pipe steam, so we tied a couple new radiators onto that. We also replaced the boiler with a more-efficient one. The owners were delighted- they heated more space on less gas!

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

    Alan (California Radiant) ForbesPC7060
  • jumper
    jumper Posts: 2,633

    I've made too many mistakes to count. Try to learn from them.

  • HVACNUT
    HVACNUT Posts: 7,852

    You're a real stickler. But I think he was just spitballing. And stop exaggerating. 95% is only 438.3 hours per year.

    bjohnhyGGross
  • DCContrarian
    DCContrarian Posts: 1,600

    Undeterred by your ribbing, I'm going to nerd out a little more. I thin Alan actually meant it meets 95% of the design load, but let's look at a few different ways that could be construed. I'm going to use weather statistics from my hometown of Boston, MA (This post explains how to get them: https://www.greenbuildingadvisor.com/question/how-to-model-and-predict-electricity-usage-for-a-heat-pump

    )

    Design temperature for Boston is 13F, at 95% of that load you can maintain comfort down to 15.4F.

    If what you really meant is 95% of the time, there are 438.3 hours per year* when you're not meeting the load. In Boston, there are 439 hours in a typical year when the temperature is 21F or below.

    If what you really meant is you cover 95% of the heating load for the year, in Boston 5% of the heating degree-days occur when the temperature is 13F or below.

    *(in non-leap years).

  • Does this house have any sort of ducted system for air-conditioning or air filtration?

    If so, possibly consider an small secondary boiler and a few fan coils to inject warm air on the coldest days. Make it automatically come on when the outdoor temperature drops below a certain set-point.

    If no existing ducted system, how about some floor-mounted Runtal or Jaga 2-3 bar radiators installed around the high heat loss area (the atrium), fed by the small boiler in 2)?

    I presume that the floor heat output into the living space can be improved simply by the addition of some R14 Rockwool with a reflective barrier on top (1"-2" air gap above the reflective barrier to the subfloor) installed in the floor joist bays that are exposed under the structure. 3/8" plywood to cover it over from below to keep critters out of the Rockwool. This would also help with any cold air leakage.

  • skyking1
    skyking1 Posts: 166

    Yes, many of them. I'm not a pro but that is no excuse.