Have You Ever Made A Mistake?
I installed this Viessmann Vitodens (172K BTU) in 1997; replaced an old Hydrotherm. In-slab radiant, ~4,000 [], 18' ceilings, floor to ceiling single pane glass windows. The house is suspended in mid air over a steep ravine. An architect's dream, a heating contractor's nightmare.
Back then, the max. temperature you could get from a Vitodens was 167℉. That year - 1997 - we had a particularly cold winter and the boiler just couldn't keep the house warm, even running at max. setpoint.
Luckily, we haven't had winters as severe, but the owners never called me back. They tore my stickers off the boiler and pump control module. Since then, the husband and wife died and the daughter has moved in. The boiler is still working even though there's been a lack of maintenance, but her insurance company is making her get a new one.
Imagine running that high a temperature water in the slab. Bare slab or tile mostly; carpet in the bedrooms.
Two btu per sq ft for degree difference for a slab
Comments
-
-
or panel radiators or even hydroair.
0 -
has the neutralizer dissolved all of the calcium?
also not so common to have a neutralizer in 1997.
everyone but the architect's nightmare.
0 -
Curious why the insurance company is requiring a replacement?
How do you plan on rectifying the situation?
0 -
-
@EBEBRATT-Ed Baseboard wouldn't really look good. It's pretty fancy inside and installing the piping under the house would be difficult. You'd need some serious scaffolding. Some nice Runtal or equal rads would work.
@mattmia2 We installed a few of those neutralizers back in the 90's. Sold along with the V. boiler. It actually doesn't need a neutralizer since it drains into the ravine. I'm sure there are some acid loving plants down there.
@kcopp The insurance companies don't want to pay for any catastrophic damage done by old equipment. They also want a seismic valve on the gas line and a water monitor on the water service.
@hot_rod The house could really do with some floor, wall and ceiling insulation along with new double glazed windows. It's just a question of money.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
So, you're doing the replacement/upgrade ?
Isnt that the tops of trees seen down thru the support framing ?
I get the idea of nature. I live in it too. As long as you cant see the neighbours house , and you have lawn, trees, birds, deer whatever… thats cool.
But,, edge of a cliff ? Hard no from me lol.
30+ yrs in telecom outside plant.
Currently in building maintenance.0 -
i bet you could get a spacepak with a hot water coil in there somewhere.
0 -
There’s also a heat sucking atrium in the middle of the house.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab3 -
-
I could have chosen a different boiler with a higher setpoint, but I don't like running radiant at such a high temperature. I believe the owners were warm 95% of the time.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
-
-
how well is the underside of the floor insulated?
0 -
If you've ever got 9 or 10 hours to spare, I'll tell you of the mistakes I've made that immediately come to mind.
I don't think is a mistake though.
This problem was engineered into the home long before you got there.
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes2 -
If you didn't design the system and all you did was replace the boiler, I'm not sure it's your mistake. Do you even know if the old boiler was heating the space either?
I go back to your signature tag, "Two btu per sq ft for degree difference for a slab." There's only so much you can get out of a slab before it becomes uncomfortable to walk on.
1 -
if the occupants are warm 95% of the time, it sounds like the system is adequate for design day condition? 5% of year at below design condition is is too cold inside?
Probably calculate that atrium square footage counting the walls at R-3 since it is mostly glass.
As @DCContrarian mentioned the floor at comfortable 82 surface is only going to get them 20- 25 btu/ sq ft depending on ambient temperature.
I doubt, even in your climate that 20 btu heats that atrium?
But, I don’t see any of this being on you?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Design day is 99th percentile. 88 hours per year.
At 95% of the time, that's 440 hours per year, or 18 days. That's a lot.
0 -
I never forget an unhappy customer. Especially when all I can say is to insulate the house better. I should have recognized the difficulty and alerted the customer before doing the work.
@mattmia2. Joists bays are exposed. i.e. no insualtion.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
since half the heat or more is going outside you could run the loops at a higher temp without the floor getting too hot.
alternatively they could insulate it with a couple inches of foam and cover it in such a way that the joists are still exposed. as a bonus they would only be paying $3k a month to heat it instead of $6k.
but if it look at what i did in 1997 when i had neither money nor experience…
2 -
-
I don't think there's enough floor to heat the place. I've run into this twice. I designed a system for my sister. Beautiful post modern in New England, glass walls single pain. The design called for supplemental heat to meet the load. Husband said no to panels or cast iron. That was a cold house.
Another one. Hills of western mass. An addition I didn't do but was called to look at. Same thing. not enough floor for an all glass cathedral ceiling. They wanted me to bring my assessment and go to court with them.
Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver
1 -
They are not mistakes, they are learning experiences. …and firing the guy that had the most experience on the job was the best thing for you Alan. Now you have all this experience to work with to solve the problem. Or you could walk away. You are in the catbird's seat now. But I'm sure you will do the right thing.
I remember firing 4 different customers in my career. One I called a crook by using his own words about me against him and asked them to call one of my competitors. There are better crooks out there than I. LOL
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
I got a call yesterday from a customer whose system we installed in 2006. He stiffed me $500 at the end of the job and I hadn't heard from him in 20 years. His Munchkin was dead and he called me out of desperation. Of course, I remembered that he hadn't paid up, but I didn't hold that against him and I went over and replaced the fuse on his circuit board and he was only too glad to get his heating and DHW back and only too glad to pay my bill. One way or another, I collect on any outstanding debts.
What this has to do with the original subject, I have no idea, but I'm feeling pretty good this evening.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab9 -
-
Interesting. My Brother and SIL lives out in Northern California. There are a lot of houses built on the side of mountains. I don’t know how folks can do it lol. I would be terrified. Honestly, with such a small percentage of uncomfortable days, a wall hung electric space heater is the perfect solution for the little gap in comfort.
Lifelong Michigander
-Willie
1 -
Another architect's dream! Plug in some portable electric heaters when it gets to cold, and keep them in a closet out of sight when not needed.
0 -
have to say that I am impressed that the system has held up give the towering sub-structure. Excellent engineering and build to attain that. Rather than pushing the spec and comfort level that system that you know is doing 100% of what it can, to supplement this place adding a Rinnai DV wall furnace would likely have solved the temporary issue. I’ve done that many times over the years.
0 -
I had a similar situation many years ago. The owners of an old house wanted to turn the deck into a four-season room. They asked about radiant, but a heat-loss calc showed not enough floor area.
The main house had one-pipe steam, so we tied a couple new radiators onto that. We also replaced the boiler with a more-efficient one. The owners were delighted- they heated more space on less gas!
2 -
I've made too many mistakes to count. Try to learn from them.
0 -
-
Undeterred by your ribbing, I'm going to nerd out a little more. I thin Alan actually meant it meets 95% of the design load, but let's look at a few different ways that could be construed. I'm going to use weather statistics from my hometown of Boston, MA (This post explains how to get them: https://www.greenbuildingadvisor.com/question/how-to-model-and-predict-electricity-usage-for-a-heat-pump
)
Design temperature for Boston is 13F, at 95% of that load you can maintain comfort down to 15.4F.
If what you really meant is 95% of the time, there are 438.3 hours per year* when you're not meeting the load. In Boston, there are 439 hours in a typical year when the temperature is 21F or below.
If what you really meant is you cover 95% of the heating load for the year, in Boston 5% of the heating degree-days occur when the temperature is 13F or below.
*(in non-leap years).
0 -
Does this house have any sort of ducted system for air-conditioning or air filtration?
If so, possibly consider an small secondary boiler and a few fan coils to inject warm air on the coldest days. Make it automatically come on when the outdoor temperature drops below a certain set-point.
If no existing ducted system, how about some floor-mounted Runtal or Jaga 2-3 bar radiators installed around the high heat loss area (the atrium), fed by the small boiler in 2)?
I presume that the floor heat output into the living space can be improved simply by the addition of some R14 Rockwool with a reflective barrier on top (1"-2" air gap above the reflective barrier to the subfloor) installed in the floor joist bays that are exposed under the structure. 3/8" plywood to cover it over from below to keep critters out of the Rockwool. This would also help with any cold air leakage.
0 -
Yes, many of them. I'm not a pro but that is no excuse.
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 135 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements