So I realize each year its a good idea to drain down and reset the air charge in these compression tanks,I have a system with 2 20 inch tanks overhead with site glasses,and each year at the start of season I drain them down because the water levels in both are almost full but not quite. The tanks are piped in parallel,each with their own shutoff valves upstream of the b&G ATF-20 tank fittings where the system is connected to them. On the opposite end there is those airtrol boiler drain type valves with a stem that rises up into tank. I just want to make sure im doing this rite because I find the tanks become quite full even before water is even heated. From my understanding you should drain each tank until you start to suck air up through that airtrol drain fitting correct? Which in my case would start at about 1/2 tank or a bit more. Before that point it just spits out solid streams of water because the water is over the tube. So I stop draining when it gets to that level, I changed site glass nuts/washers/gaskets,so when I open up system valves,pressure in system dropped down to 6 to 8 psi and I started bypassing the prv to bring system up to 12,but the level in my tanks were rising as well while doing this. I also opened the drain on the atf-20 fittings while filling system back up,as the instructions say to have that vent/drain open while filling to push air out,and close it once a solid stream of water occurs. So I did that as well. But I guess my problem is the level in the tanks ended up around 3/4 up the glass roughly. And system was around 86f at the time. So im worried what the level will be once water is 200f. I tightened all fittings around gage glasses,packing nuts,ect. Because my thoughts were I may be losing air somewhere causing it to keep filling. But didnt seem like It was. Where do you guys like to see the tank levels,I know not all have gauge glass but am I doing something wrong maybe? Thanks
Almost. The tank should be drained until it is empty. Completely empty. Then when you open it back to the system, water will compress the air and give you your cushion. The Airtrol will, if all is going well, attempt to maintain that more or less half full condition when the system is under pressure.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
If your system is intact and has no leaks you should not have to refill it OR drain it every year BECAUSE this allows excess oxygen to enter the system and you do not want that ever if your system has no leaks.
Why are you running your high limit to 200 Degrees Fahrenheit when 170-180 degrees Fahrenheit will do if you have baseboard heat???????
How much water do you have in your system?
Is your fill valve shut off completely? If not, it should be.
Have you reached a point where you have had a screaming vacuum leak when you started a circulator and traced it back to the sight glass packing gland nuts???
You have to remember that you are compressing the air in the tank when the water in the system expands when the boiler is heating the water so that is not a problem.
1 -
Forget about the gauge glasses. Don't even look at them. Drain both tanks completely, as Brother Jamie said.
The boiler should be cold while doing this. After the tanks are empty and you open the valves to pressurize them, the Pressure Reducing Valve should fill the system to 12 psi. Regardless of the level in the glass. Don't look. If you notice the system over filling past 12 psi (like approaching 15 psi), shut off the feed valve and get a 0-60 psi gauge with a hose adapter to check the accuracy of the boiler gauge.
Now turn the power on and run the heat. Make sure all radiators heat and pressure doesn't rise above 15-20 psi at 180° water temperature. 180° should be limit. No need for 200° unless its colder than design day temperatures. Which is almost never.
If you think the tanks might be filling too quickly, are there any air eliminators on the boiler, or an indirect water heater?
My method is to drain the system. Fill the boiler to operating pressure with the tanks isolated. Once the boiler and system are full and pressurized open the tanks.
The top gauge glass washers are prone to leak and dry out because the never see water so changing them every few years is a good idea.
I wouldn't stress about the tank level unless the system over pressurizes from a water-logged tank. You could close both gauge glass valves to prevent any loss of air and just open them if you want to check the water level but most jobs don't even have a gauge glass.
1 -
Rite,last year i did close the valves because I thought maybe I was losing air through the valves or gaskets, this year i replaced nuts, gaskets and left open so far,I do like to see the level rather than grabbing a 10ft ladder to knock on tank. My thought is not to drain the entire tank though,as I dont want to have to add much if any fresh water. But I still find when I open the valves to the tanks my system pressure drops too low and still have to make up,and instead of pressurizing the air space and raising system pressure,the level rises to 3/4 or slightly more. Im now wondering if wrong size atf valves were installed. Im gunna go back and measure tanks.
If you replaced the compression tank with a diaphragm or bag type expansion vessel, it would be 1/3 the size and allow to to add a good microbubble air removal device.
If it takes on water throughout the year, it may have a small leak somewhere.
Living the hydronic dream1 -
You may not want to drain the tank all the way — but unless you do, and the tank starts empty at atmospheric pressure, that style tank isn't going to work properly.
Much larger tanks of that style — called hydropneumatic tanks — were equipped with an air valve and an air compressor to maintain the proper air cushion in the tank. That's overkill here.
As @hot_rod notes, it can be replaced with a diaphragm style tank, which is smaller and, until it fails which it will, does much the same job if it's sized properly.
Well I hearya there, it would have to fit up in same place as these 2 tanks and be 2 tanks same shape which ive never seen in a diaphragm or bladder tank. As for air removal, not gunna get much better than what I already have here,5" Rolairtrol with air outlet piped to the compression tanks. Its a good setup if no air leaks out. Theres certainly no water leaks on system.
Ok im not saying you guys are wrong,trust me. Im just confused why b&g states if tank is empty, start filling leaving vent valve on the atf open until a solid stream of water is coming out,then close vent valve and let system pressurize to cold fill pressure. Ive always been one to rtfm and do everything I do correctly. So this bugs me. And if you read the older manual for the drain o tank valves it says to drain a waterlogged tank until water level reaches dip tube and stop draining. But then I just looked up the new drain o tank manual and its like they changed their minds over the years? Because now I see it says it allows you to drain tank completely and seems to only come in one size now where back when these tanks were installed it came with a very long coiled copper dip tube which you had to cut to size for whatever tank you have,in my case it was 13" for a 20" tank. Interesting
Well the glasses are there so kinda hard not to notice my tanks filling up past where I think they should,ya know? This is how it was installed in 2006,I did not install these tanks. I have a 5" rolairtrol that feeds any air into the 2 tanks. No boiler and no other air eliminator on system. Its a steam to wtr hx. And as far as my design temps,you guys kill me. How are you guys going to tell me what temps to run when you have no idea what type of system /building im working with. But my design is in fact 200f at 35f and below. Thats not what my questions are. I will try and drain tanks completely and see if I end up at a more exceptable level and keep my pressures down but I was only following instructions from b&g so I guess they are wrong.
Ok so I understand i dont wanna be draining system down every year and adding fresh water. Im very familiar with water chemistry. Im not a new tech,just never had any issues with these very rare in my area compression tanks. But ive come across them before and yes have had to drain many,but never had the problems im having with these. They do get waterlogged. Theres no avoiding it. Just frequency is my concern and my pump suction pressure rising to 28 or so by end of season if I remember correctly from last year. As far as design temps,please dont be one of those guys. This post is not about temps its about tanks getting too full and increased pressures each season by end of season. I do need 200f water under 35f o.a.t. its on reset. From 140 to 200f. 60 to 35f. I do not know total system volume. I can only hope they were sized correctly. Im going to try as others mentioned and drain tanks completely but that kinda goes against b&g instructions. Yes i have prv isolated due to this problem so that could be ruled out. Screaming vacuum leaks at gauge glass when pump kicks on? Thats not a possibility and not sure what you mean. All parts of system are positive pressure just like you'd expect on every hydronic heating system. Im more worried im losing air at the gauge glasses which is why I shut them off last year but didnt seem to help. Could be they dont close tightly though and I need to either get rid of them or put brand new valves in.
some dish soap in a spray bottle will tell you if your gauge glasses are leaking. Could be any of 100 other things at a high spot in the system that is leaking air that collects there too. Depending on where the air separator is, air could prefer to collect in other places. There also could be an automatic air vent hidden somewhere or even someone bleeding it with a manual bleeder that you don't know about. This is some sort of industrial system which is not what we usually see here so we made assumptions based on it being a typical residential or small commercial system.
You have an air management system not an air elimination system.
My home heating systems steel compression tank is almost 3/4 full and it works fine with one circulator operating at 12 P.S.I.G. pushing hot water through 225 feet of 3/4" fin tube baseboard in a poorly insulated house.
Do you know which model Rolatrol air separator you have for your heating system?
You have either an R series with strainer or RL series without a strainer
If you have an R series how often have you removed the strainer in the Rolatrol air separator to clean it??
If you can provide pictures of all the near boiler piping that would be a great help to help us help you.