Puffback/delayed ignition

Options

I have a AFII 85 burner. First few fires of the season it ran perfectly fine. Now I'm noticing a slight puffback/delayed ignition on start up. I have replaced or changed or verified operation of the following; fuel filters, pump strainer, pump solenoid, electrodes, constant 120v to transformer, and did pressure test off pump. Have a burner control module on order as it seems the timing may be off for the firing sequence. Anything else anyone suggests?

Comments

  • mattmia2
    mattmia2 Posts: 18,449

    what did the combustion analysis show?

    Robert O'Brien
  • Steve214
    Steve214 Posts: 23

    Have you checked the spark? It’s a little difficult on the AF2 (my second favorite right behind the NX…not!) Sometimes that air dial breaks too. Too much air and it won’t light, some are finicky with the incorrect nozzle.

    HVACNUT
  • HVACNUT
    HVACNUT Posts: 7,815

    You ordered a new primary because the existing one took it upon itself to change pre purge from 15 to 18 seconds? Thats a talented primary.

    EdTheHeaterMan
  • Sask123
    Sask123 Posts: 11

    @mattmia2No one in 500km of me has a combustion meter that will bother with an oil furnace.

    @Steve214 I haven't checked spark no, how do you test it on those with the wire leads? Air dial is set on 5 which is what plumber set it on when installing. Has no problem lighting just have a puffback everytime it fires.

    @HVACNUT you bet. T= R x C. Do you know how control boards work?

  • mattmia2
    mattmia2 Posts: 18,449

    then where are you getting oil from? modern oil burners need to be set up with combustion analysis instruments. if someone is distributing oil in the area then there has to be an oil burner tech setting up burners.

  • Sask123
    Sask123 Posts: 11

    @mattmia2 bulk fuel distributor, they don't know anyone in their coverage area working on them.

  • Grallert
    Grallert Posts: 1,251

    If you are doing your own service which is fine I suppose, You really should get your own combustion analyzer including a smoke spot tester. An oil burner or any fuel burner for that matter really can only be set up by knowing those numbers. This would be a good investment. Anything else is a guess.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

    GGrossSuperTechEdTheHeaterManold_diy_guy
  • Sask123
    Sask123 Posts: 11
    edited October 27

    @Grallert yes just not willing to spend 1000$ on one to use it once. Trying to convince a local business guy to buy one. And they obviously aren't needed if no one owns one in the area, called 15 companies not one of them had a combustion analyzer.

  • Grallert
    Grallert Posts: 1,251

    It used to be that a service person could open the door to a boiler or furnace and have a look at the flame and and listen to the sequence of operation of the burn and be able to tell sort of how it was running. Back when you could practically climb into the combustion chamber that approach got you heat. Those boilers are mostly gone now. Nowadays you need to know exactly what's going on on the combustion side of things and you can't do that by eye or ear anymore. Sure you might get lucky.

    " yes just not willing to spend 1000$ on one to use it once" The boiler should be service at least ever couple of years and every time should be tested. Things change in there and it doesn't take much to throw the whole thing out of whack.

    Sounds like you have a delayed ignition.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

    mattmia2
  • MaxMercy
    MaxMercy Posts: 632

    If you maintain your own oil burner, you won't use it just once - you will use it every time you service it. A modern digital analyzer is expensive, but you can still find an old Bacharach "wet kit" which is good enough for what you're doing. Wet kits are very inconvenient because while the digital analyzer spits out all combustion parameters pretty much in real time (so you see immediately what your air settings are doing), a wet kit will only show your CO2 for every physical sample drawn, which takes about 30 seconds, Move the air shutter? Take a sample. Not right? Move the shutter and take another sample.. rinse and repeat. You will also have to draw your own smoke samples separately which take another 30 seconds or so. Pros won't use them anymore, but wet kits are at least plenty accurate for what you need and never require periodic calibration or sensor replacements.

    GrallertGGrossbburd
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,370

    @Sask123 I agree with @MaxMercy find an old Bacharach wet kit on E-Bay or market place and a smoke tester . You will probably have to buy new fluid and fix it up and get a smoke tester

    MaxMercySask123
  • Grallert
    Grallert Posts: 1,251

    One could also do a little "under the table" combustion analyzing to offset the cost of the tool. I wouldn't know anything about that.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

    MaxMercySask123
  • mattmia2
    mattmia2 Posts: 18,449

    some of the more inexpensive combustion analyzers are around $400-$500

    Grallert
  • HVACNUT
    HVACNUT Posts: 7,815

    @Sask123 , you said you tested pump pressure. What was it? You also said "slight puffback/delayed ignition". Which is it? A delayed ignition will happen for many reasons. A puffback is something where you'd be looking for quotes on home remediation. Then you said, "the timing may be off on the firing sequence" of the primary. No. That's not how it works.

    And what equipment is this AFII 85 in? Lennox furnace?

    See if its acceptable the appliance can be converted to gas, then get the conversion done. I assume there's a plethora of gas heat techs with combustion analyzers in your area.

    I'll give you one safe test to try. The AFII has an opaque window looking down the rabbit hole, I mean air tube. Unplug the oil valve, start the burner, and put a peeper to the window to see if there's spark. I don't know what primary you have. Some will spark during pre purge. Others will wait for the countdown to zero. So if you have a modern primary you have either 30 or 15 seconds to look.

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,030

    You should start at least two different discussions on the same subject to see if you get different answers fro the same question. I will tell you that you don't need a professional if you live in the sticks in Canada

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Sask123
  • Sask123
    Sask123 Posts: 11
    edited October 28

    @mattmia2 which brand do you recommend in that price range?

    @HVACNUT pump pressur was 110 says it should be 140. It would be delayed ignition then. Do you mind explaining how it works then? A bad resistor is a control board 100% will cause a longer delay.

    Yes it's a Lennox furnace. And that's my other option is to just get propane. Was quoted $ CAD which is obsurd considering how simple the installation would be.

    The primary is a 7505 B1500. I will try that to check for spark tho. I also read that it is was recommended from Beckett to upgrade to one with post purge as the residual heat in chamber would cause nozzle to drip. Not sure if that one has post purge or not but the new one is 7505 B1500U and has post purge

    @EdTheHeaterMan

  • mattmia2
    mattmia2 Posts: 18,449

    tpi? others would know if it is missing something important. i just used it for a modcon boiler, oil is more complicated, temps and draft are important on oil, on a mod con you mostly just need to look at the stoichiometry.

  • SuperTech
    SuperTech Posts: 2,728

    The Testo 310 or an analyzer from TPI would be my recommendation for a low cost combustion analyzer. I doubt the primary control is your issue, they don't malfunction in that manner. But if you are going to swap it out I would recommend installing either a Resideo R7284U or a Carlin 70200. Both of these have a digital display and can help make troubleshooting easier.

    The pump pressure being set incorrectly is a concern, that didn't happen on its own. You are definitely going to need a combustion analysis if you correct the pump pressure.

    I have taken the entire nozzle and electrode assembly out of the AFII and observed the spark by running the burner with the solenoid unplugged on the oil pump. You can also check the igniter by measuring the resistance between the two wires that go to the electrodes and then measuring the resistance from each wire to ground. Resistance should be the same measuring each wire to ground and the sum of the two measurements to ground should equal the measurement taken between the two wires.

    Sask123
  • HVACNUT
    HVACNUT Posts: 7,815

    The 7505B does not have post purge. That would be a "P". Did you throw off the Z dimension replacing the nozzle?

  • Sask123
    Sask123 Posts: 11

    @SuperTech which TPI one would you recommend? Both brands have their combustion analyzers 5% here in Canada right now.

    @HVACNUT if i remove the jumper and get the BeckettLink Pro I am able to reprogram. No I used wrench on the nozzle adapter side when tightening and loosening. The contractor that installed it the time before me though did not use a wrench on adapter when tightening nozzle tip back on. I used a z2000 gauge to set the nozzle depth from the FBX head and then slid it up 1/16th like it says on Becketts site though so that should be fine. Used a reloading caliper today again to verify electrode measurements. Think I am just gonna pull the pin and buy a combustion analyzer, there is a guy south of me that will come but will cost 500$ plus tax for travel alone….

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,030

    People that live in the sticks should not purchase anything that can't be serviced by the average untrained handyman. If you want to have high efficiency equipment then move to a more populated area where there at least 2 companies with a combustion analyzer.

    That said, let's see if we can help you with your problem.

    That AF II burner is kind of finicky when it comes to proper adjustments. And that Lennox furnace has an observation port that does not allow a good view of the flame in the combustion chamber.

    So, we need to start somewhere, and I would start with the ignition transformer.

    There is an easy way to test the ignition transformer. It is not foolproof, but I have used this method for years, and it has served me well.

    Using a screwdriver with a good quality plastic handle, you need to see if the spark will jump at least 1/2 inch. Then, slowly pull the screwdriver away from the terminal. The spark should continue until it can be stretched across a 1-inch gap.

    This proves the transformer's ability to produce a strong spark, even if the fan is blowing. The larger the gap across which the spark continues, the better indication you have that the coil windings are in fairly good shape and should last another season.

    image.png

    The AF II burner uses wire leads so I would use 2 screw drivers than will insert into the spade connectors lis illustrated below. The same measurements for the jumping spark apply. Start before you reach a 1/2" gap and pull to at least 1"

    Screenshot 2026-11-05 at 4.09.45 AM.png

    this is not how the schools tell you to test spark but this is how I did it for over 40 years,

    I think you are going to find that your electronic ignitor is fine. but that is where I would start.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • SuperTech
    SuperTech Posts: 2,728

    I can't remember which model TPI analyzer I used, it was several years ago and it was provided by a previous employer because TPI was the least expensive combustion analyzer they could find. It got the job done. I use a Testo 300LL but I have used the 310 before and it was accurate. For a homeowner using it on your equipment and inexpensive TPI analyzer is probably a good option.