Old cheaper Main vent valves.

Options

So I have a new Utica gas steam boiler with the older cheaper vent valves on the Mains and i was wondering if I went with a Gordon #1 if there would be any difference in the way the radiators heat up. The system right now works very good.

Comments

  • mattmia2
    mattmia2 Posts: 18,399

    it depends. look at how long it takes for the ends of the mains to get hot from when the boiler starts steaming. if it is a couple minutes then the limiting factor is probably the mass of the mains. if it is like 10 minutes plus then you could probably use more venting.

    also make sure they close when they see steam.

  • Steamhead
    Steamhead Posts: 19,007

    @roadmaster , how long are the mains and what pipe size? What vents are on them now?

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

  • The two mains are 20' in length each. They are 2" black pipe. The air vents are maid of mist. I have read some good reviews on the Gordon #1 vent valves. Thanks

  • Steamhead
    Steamhead Posts: 19,007

    The Gorton #1 would be a good choice for those mains.

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

    ethicalpaul
  • STEAM DOCTOR
    STEAM DOCTOR Posts: 2,680

    Before you spend the money to replace the existing main air vents, you should pull them off and try to blow through them. If you can blow through them smoothly, and they're not leaking Steam, then there is no reason to replace them. The mom number one and the Gorton #1 have the same capacity. Which MOM do you currently have?

    ethicalpaul