Overfilling boiler
I have a SGO-3 Weil McClain steam boiler it has no automatic water feeder two shut off valves to add water i have a return line that leaks but not real bad that I have to fix but the boiler is overfilling at least once a day I have to drain like 4 pails of water out of it I have no idea how water is getting in it
Do you have a 2 pipe system with a condensate line buried in concrete???
Is there a domestic hot water coil in the boiler? Or an indirect water heater hooked up somehow? Either of those can leak domestic water into the boiler.
Otherwise, somewhere there is a connection from your domestic water to your boiler which is allowing water to get in. What kind of shutoff valves are you talking about? If they are ordinary globe valves or older gates, that's the first place I would look.
I would add that getting that much fresh water into your boiler every day is going to guarantee a short and miserable life for it…
Based on the limited information, (no auto feed), this sounds like a passing manual feed valve.
Can you take a photo of the boiler and the water feed line with the 2 manual valves and maybe more photos from farther back so we can see all the pipes from floor to ceiling near the boiler
EDIT: Two manual water feed valves sounds like an old valve may have failed and rather than replace the bad valve someone added a second valve. perhaps the second newer valve is now going bad.
Good morning to you Ed
That was my first thought; but I figured I would ask if it was two pipe system first.
- 87.8K THE MAIN WALL
- 133 Chimneys & Flues
