A small apartment building currently has an A.O. Smith Burkay 120,000 BTU boiler directly heating a 75 gallon storage tank (not an indirect) and the boiler needs to be replaced. That boiler doesn't seem to be made anymore and it would be nice to use the existing 6" flue rather than going high efficiency PVC up the side of the building. Any suggestions for a replacement boiler?

Since the Burkay has no storage, it's short which helps with the flue run. It's basically a copper heat exchanger sitting on top of a flame.

8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab

Comments

  • hot_rod
    hot_rod Posts: 28,524

    a copper tube boiler from Lochinvar, RBI, Raypack with a plate HX and use the existing tank. Similar to the EK system.

    How old is the tank? EK builds the package to connect to any boiler.

    No way to fish a mod con flex vent up the 6"

    Screenshot 2026-09-23 at 4.03.54 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Alan (California Radiant) Forbes
  • HVACNUT
    HVACNUT Posts: 7,744

    A.O. Smith has a 71 gallon 120,000 btu commercial water heater.

    Alan (California Radiant) ForbesBig Ed_4
  • mattmia2
    mattmia2 Posts: 18,231

    htp makes some similar stuff too. with the cost of commercial water heaters, the htp stainless tanks are probably competitive now.

  • mattmia2
    mattmia2 Posts: 18,231

    you could probably do something with a tankless water heater and a circulator too. There are tankless models that are only 85% efficient or so that use a conventional vent if getting a direct vent outside is an issue.

  • hot_rod
    hot_rod Posts: 28,524

    The Rinnai Demand Duo was built for hotel and apartments

    High efficiency and endless water

    How many units, how much DHW fo they need or want?

    Tubs? Older high flow faucets?

    https://www.rinnai.us/commercial/demand-duo

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • GroundUp
    GroundUp Posts: 2,571

    Laars Mini Therm JVS-125 has a 6" flue and sounds pretty similar to what you have going on with the copper HX. I have the JVS-100 in one of my buildings running baseboard for 5 units and a 120 gallon indirect, going on 7 years now with nothing to complain about.

    Alan (California Radiant) Forbes
  • Hi, I think I'd start with a survey of the fixtures to see what could be done with the demand side. Once done, just possibly a light commercial tank-type heater could be piped (recirc?) to keep itself and the existing tank hot.

    Yours, Larry

  • 8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    Lyle {pheloa} Carter
  • GroundUp
    GroundUp Posts: 2,571

    Whoops, looks like they call it a JX now. Actually mine may even be a JX? Heck, good question! But yes they definitely make a JX-125 with a 6" flue.

    Alan (California Radiant) Forbes
  • hot_rod
    hot_rod Posts: 28,524

    what about running a load calc to see what what size system you need

    https://iapmo.org/we-stand/water-demand-calculator

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Alan (California Radiant) Forbes
  • HVACNUT
    HVACNUT Posts: 7,744

    Amazing @Alan (California Radiant) Forbes . I don't think I've ever seen that boiler before you started this thread. Today I show up at a house that air filters were owed from the maintenance, and what do I see in the basement?

    20260924_101000.jpg 20260924_101103.jpg

    This one is feeding a 119 gallon indirect.

    Alan (California Radiant) Forbesmniskamattmia2Intplm.
  • HomerJSmith
    HomerJSmith Posts: 2,833

    Laars JX series boilers gives a variety of BTU ratings to match your needs. Not to run it with street water, tho, lots of O2. Need a heat exchanger & two pumps.

    If the current sys satisfies morning & evening hot water needs, go with what's there. You may be able to boost tank temp with a Caleffi Angle Mix valve. You may have to install a back flow valve and Expansion tank depending on regulations.

    San Francisco is a temperate climate running a 4" vent into a 6" B-vent may not pose a buoyancy exhaust problem if 6" boiler venting isn't available. If the existing venting is round and a straight shot to the roof you could run a 4" thru it. I've done that. I've just supported the 4" with plumber's tape.

  • mattmia2
    mattmia2 Posts: 18,231
    edited September 24
  • jumper
    jumper Posts: 2,624

    Owner will save electricity with storage heater. Do the arithmetic. You can save gas with tank heaters in series.

  • plumbworker
    plumbworker Posts: 34
    edited September 27

    i'm pretty sure ao smith still makes some ideration of that boiler, but likely doesn't meet ultra low nox requirements in the sf bay.. @HVACNUT i believe is on the right track. might make sense upgrading to a commercial water heater.. is there any wiggle on the 6" flue? seems like a wh might be simpler than using a boiler designed for space heating with some type of hx. The Ray Pak hdss copper fin is rated for dhw (pace stocks bronze headers fitted with ss pump and 150psi relief valve) and the flue connection is 4" (will likely need to add a barometric damper) lowest input is around 150k…

    Alan (California Radiant) ForbesHomerJSmith
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,169
    edited September 27

    @HVACNUT

    back in the day almost every school I ever did service at had going back 50 years or more had an AO SMITH Barkay heater piped to an asbestos covered storage tank. I guess they held up pretty well, but I noticed they always seemed to short cycle a lot.

    Seems that the smallest one they make now is 300,000 input.

    HVACNUT