Flow Settings for Home Run Piped Emiiters with TRV

Options
tropostudio
tropostudio Member Posts: 42

Quick summary of my hydronic heating system, commisioned in 2018:

59 KBTU/h heat loading at coldest design day. 80 KBTU/H mod con, fire-tube boiler. Calculations are for 30F Delta T and 140F supply/110F return for -10F design day.

A single Grundfos Alpha Circulator (no P/S pump). 15 home run emitter loops - 5 per floor, distributed via Uponor SS manifolds. 12 loops use 3/8" PEX, 3 loops loops use 1/2" PEX.

I've calculated a 3.9 gpm system flow; 0.70 ft. head loss across combined parallel loops w/ emitters; and 2.06 ft. head loss across largest single loop with emitters. Every panel has an Oventrop TRV.

Here is how I have been setting loop flows: First, I set each TRV at '5', which should have them 'wide open' while I set flows. I run the Alpha at it's lowest constant pressure mode setting, which ostenibly maintains 6 ft. head. This is well above the calculated drop for my total system, but is as low as the Alpha will go I then adjust each loop's flow valve to match my calcs. Calculated loop flows range from 0.1 (a bathroom) to 0.5 gpm (living room).

I still have a nagging feeling I missed something in how I balanced it. The flow and head loss calcs include an equivalent length allownace for a 'valve' at each loop, but how do you actually account for the fact that each loop has a flow valve and a TRV - with the pressure drop across the TRV varying over time? Should I be following a different procedure

FWIW, my TRV's are set to '3' (68F) and I leave them alone. The house temps stays at a consistent 68F all Winter. The house is quite tight and well-insulated. The system generally just cruises along, with very little ramping up and down (except after the indirect DHW steals a call for heat).

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 27,775

    Don't overthink it. If your TRVs are controlling the space temperatures the way you want them… what's not to like?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • hot_rod
    hot_rod Member Posts: 28,256

    the TRVs and the Alpha should do the balance for you.

    TRVs are proportional valves, not open / close like zone valves.

    If the Alpha is getting the job done at its lowest setting, what’s not to like?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream