Zone control

Options

What is the benefit of the taco zone controllers on hydronic heating? I've seen a bunch of buildings with zone valves wired directly in the boiler room. Is there more of a benefit besides easier wiring?

Owner

Steamnowrockford.com

Comments

  • Jamie Hall
    Jamie Hall Posts: 27,911

    mostly more flexibility — and simpler wiring (if it's done right in the first place, of course). As well as some other control options (DHW override, for instance).

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    SteamNow
  • hot_rod
    hot_rod Posts: 28,543

    simplified wiring, indicator lights, fused protection of the transformers

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream